Re: Electricians: Tough one for you
[Re: adam m]
#6671968
11/21/19 06:49 PM
11/21/19 06:49 PM
|
Joined: Nov 2015
Posts: 16,951 OH
Catch22
trapper
|
trapper
Joined: Nov 2015
Posts: 16,951
OH
|
Electricity scares the bejebbers out of me, saw some stuff when young. Thinking though, maybe it's a internal issue with the welder, not the breakers.
I wonder if tap dancers walk into a room, look at the floor, and think, I'd tap that. I wonder about things.....
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6671977
11/21/19 06:56 PM
11/21/19 06:56 PM
|
Joined: Dec 2010
Posts: 34,903 Central, SD
Law Dog
trapper
|
trapper
Joined: Dec 2010
Posts: 34,903
Central, SD
|
Not sure a GFI is the right thing for a welder I had one on my chicken coop line but the water heater kept popping it and thats way less of a draw
Was born in a Big City Will die in the Country OK with that!
Jerry Herbst
|
|
|
Re: Electricians: Tough one for you
[Re: Law Dog]
#6671981
11/21/19 07:00 PM
11/21/19 07:00 PM
|
Joined: Dec 2006
Posts: 3,474 Northern Ohio ...
Sullivan K
"Keith"
|
"Keith"
Joined: Dec 2006
Posts: 3,474
Northern Ohio ...
|
Not sure a GFI is the right thing for a welder I didn't read this as the welder was set up with a GFI. I thought he was only referring to the 110 recepts being on a GFI.
My name ain't Keith
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6671982
11/21/19 07:03 PM
11/21/19 07:03 PM
|
Joined: Sep 2015
Posts: 343 NW Wisconsin
Muskrat Love
trapper
|
trapper
Joined: Sep 2015
Posts: 343
NW Wisconsin
|
Adam,
Do you know if he has a second breaker box in the shop? Also, what gauge wire did he run from the main beaker ( in the house), to the shop??
If he has 100 amp service in the shop and has the 220 plug with the proper sized breaker (NOT 20 AMP), it should not trip unless there's a short somewhere! My Miller and 7 hp compressor are each on the own breaker.... I'm thinking 40 amp for the compressor and a 60 for the wire feed, as I'm not down the shop now.
Had a fan/light combo above our range when we built our home.... About 10 years later we installed a combo above stove microwave, fan, light unit. If the wife had a caserolle in the microwave for anytime longer than 8-10 minutes the breaker would trip.
I found out that the the original light/fan unit was on a 15 amp breaker.... Guy at Menards said "Just replace with a 20 amp breaker"!
When I double checked it was wired with 14 gauge wire, which was correct for the 15 amp breaker, but a 20 amp breaker is for 12 gauge wire...... I ran a new 12 gauge wire wire to the unit, with a 20 amp breaker, and zero issues.
Hope this helps you
"I'm an old dog, and these are all new tricks!"
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6671983
11/21/19 07:03 PM
11/21/19 07:03 PM
|
Joined: Dec 2006
Posts: 8,173 Piney va. soon be 19
cotton
trapper
|
trapper
Joined: Dec 2006
Posts: 8,173
Piney va. soon be 19
|
check all the ground connections
or maybe his welder is putting power to the ground
John 3/16
ifin your gonna be dumb ya gotta be tough VTA life member
|
|
|
Re: Electricians: Tough one for you
[Re: YamaCat]
#6672025
11/21/19 07:56 PM
11/21/19 07:56 PM
|
Joined: Feb 2014
Posts: 13,150 Ky
jbyrd63
trapper
|
trapper
Joined: Feb 2014
Posts: 13,150
Ky
|
Loose ground or Neutral in panel X2 Is the shop fed from the panel in the house? Or does it have its own meter base. But sounds like a loose grd or neutral. Under the bar . Tighten all screws. Tha
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6672061
11/21/19 08:33 PM
11/21/19 08:33 PM
|
Joined: Feb 2014
Posts: 25,694 nm
adam m
OP
trapper
|
OP
trapper
Joined: Feb 2014
Posts: 25,694
nm
|
Antelope Montana, not sure but I'll ask. This shop has its own panel as it sits about 75'+ away from the house. We'll check the ground and neutrals the next time I go over
Last edited by adam m; 11/21/19 08:35 PM. Reason: Stupid phone put wrong words
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6672070
11/21/19 08:38 PM
11/21/19 08:38 PM
|
Joined: Dec 2006
Posts: 3,474 Northern Ohio ...
Sullivan K
"Keith"
|
"Keith"
Joined: Dec 2006
Posts: 3,474
Northern Ohio ...
|
What do you mean Sullivan? I know he does have 110's on the booth sides of the 220 but at counter height for his work benches. You have two 110 legs feeding your panel. I was suggesting switching your receptacles to the other 110 leg. The loose neutral/ground suggestion is certainly legitimate also
My name ain't Keith
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6672072
11/21/19 08:40 PM
11/21/19 08:40 PM
|
Joined: Mar 2019
Posts: 1,497 Southern NJ
maintenanceguy
trapper
|
trapper
Joined: Mar 2019
Posts: 1,497
Southern NJ
|
I think the GFCI's are working properly. If a toaster is plugged into a GFCI, the electricity flows out of the receptacle to the toaster on the black, hot wire. It flows through the toaster and then back to the receptacle on the white, neutral wire. Actually, since house electric is alternating current, the flow of electric keeps changing direction but at any moment, the electricity flowing out on one wire should be the same as the electric flowing back on the other wire. If the flow of electricity on the hot and neutral wire isn't balanced, it means electricity is going somewhere it shouldn't - possibly through a person.
A GFCI monitors the flow on the hot and neutral wire. If they are the same, all is good. If they are different, it opens the circuit so nobody gets killed.
When there is a big surge in electric flow (like a welder striking an arc) it causes spikes and dips in the flow of electricity everywhere else. If wires or transformers are undersized, these spikes and dips are more dramatic because the available electricity isn't enough to "fill in" the dips.
What's a capacitor? A capacitor is a device that can store electricity for a very brief time. Inductors can also store electricity. Lots of electrical equipment, including wires, have a little capacitance and a little inductance and can store a little bit of electricity. When there is a big spike or dip in electrical flow on on wire, that stored electricity can continue to flow on the other wire for a very brief time - fractions of seconds. If that happens, you have an imbalance. When you have an imbalance between the neutral and hot wire, a GFCI will trip opening the circuit.
I suspect that the wiring to the main panel is undersized or the transformers at the utility pole is undersized. It's also possible that everything is sized correctly and GFCI's just stink. GFCI breakers are more trouble then they are worth - in my opinion.
-Ryan
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6672076
11/21/19 08:44 PM
11/21/19 08:44 PM
|
Joined: Dec 2006
Posts: 3,474 Northern Ohio ...
Sullivan K
"Keith"
|
"Keith"
Joined: Dec 2006
Posts: 3,474
Northern Ohio ...
|
The 110's that are on one 20 amp circuit. If the receptacles are on just one breaker then they are only on one leg of the 220 volt service. You do not have the receptacles divided up between the two legs of the service. What i was suggesting is that you just switch the 110 receptacles to the other leg of the service
My name ain't Keith
|
|
|
Re: Electricians: Tough one for you
[Re: maintenanceguy]
#6672099
11/21/19 09:13 PM
11/21/19 09:13 PM
|
Joined: Dec 2007
Posts: 5,514 Orergon
alaska viking
"Made it two years not being censored"
|
"Made it two years not being censored"
Joined: Dec 2007
Posts: 5,514
Orergon
|
I think the GFCI's are working properly. If a toaster is plugged into a GFCI, the electricity flows out of the receptacle to the toaster on the black, hot wire. It flows through the toaster and then back to the receptacle on the white, neutral wire. Actually, since house electric is alternating current, the flow of electric keeps changing direction but at any moment, the electricity flowing out on one wire should be the same as the electric flowing back on the other wire. If the flow of electricity on the hot and neutral wire isn't balanced, it means electricity is going somewhere it shouldn't - possibly through a person.
A GFCI monitors the flow on the hot and neutral wire. If they are the same, all is good. If they are different, it opens the circuit so nobody gets killed.
When there is a big surge in electric flow (like a welder striking an arc) it causes spikes and dips in the flow of electricity everywhere else. If wires or transformers are undersized, these spikes and dips are more dramatic because the available electricity isn't enough to "fill in" the dips.
What's a capacitor? A capacitor is a device that can store electricity for a very brief time. Inductors can also store electricity. Lots of electrical equipment, including wires, have a little capacitance and a little inductance and can store a little bit of electricity. When there is a big spike or dip in electrical flow on on wire, that stored electricity can continue to flow on the other wire for a very brief time - fractions of seconds. If that happens, you have an imbalance. When you have an imbalance between the neutral and hot wire, a GFCI will trip opening the circuit.
I suspect that the wiring to the main panel is undersized or the transformers at the utility pole is undersized. It's also possible that everything is sized correctly and GFCI's just stink. GFCI breakers are more trouble then they are worth - in my opinion.
Now this right here is so well written, and complete, that I am impressed. Not an easy thing to do! I would also place money that it is correct, and the answer to your problem is contained, there-in.
Just doing what I want now.
|
|
|
Re: Electricians: Tough one for you
[Re: adam m]
#6672250
11/22/19 12:03 AM
11/22/19 12:03 AM
|
Joined: Mar 2014
Posts: 4,369 N.C MO
TONY.F
trapper
|
trapper
Joined: Mar 2014
Posts: 4,369
N.C MO
|
x2 on a loose ground or neutral they make weird things happen when they get loose also check the ground rod itself corrosion can make them loose ground same with extremely dry dirt