hot water baseboard heat. #6680253
12/01/19 07:23 AM
12/01/19 07:23 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
ours in the newer house is not heating correctly.runs good but not getting the amount of heat out the radiators we should.

tell me what you can and what we should be doing.

my thoughts are there is air in the system and it cant hold heat like water.

remember i'm a lifelong trapper mentality and i'm sensitive.









Re: hot water baseboard heat. [Re: pcr2] #6680255
12/01/19 07:31 AM
12/01/19 07:31 AM
Joined: Feb 2010
Posts: 19,719
pa
H
hippie Offline
trapper
hippie  Offline
trapper
H

Joined: Feb 2010
Posts: 19,719
pa
My place has the old radiators and if what your describing happens, I bleed the air out so I think your guessing right.

Mine have bleeders just like brakes on a car. Not sure about base boards tho.

Re: hot water baseboard heat. [Re: pcr2] #6680259
12/01/19 07:44 AM
12/01/19 07:44 AM
Joined: Sep 2011
Posts: 541
IL
G
goatman Offline
trapper
goatman  Offline
trapper
G

Joined: Sep 2011
Posts: 541
IL
Baseboards should have bleeders on one of the ends.

Re: hot water baseboard heat. [Re: pcr2] #6680264
12/01/19 07:56 AM
12/01/19 07:56 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
wife isn't havin my usual"put more clothes on" answer.thanx guys i'll be lookin in a bit.









Re: hot water baseboard heat. [Re: pcr2] #6680265
12/01/19 07:56 AM
12/01/19 07:56 AM
Joined: Dec 2006
Posts: 20,033
SEPA
L
Lugnut Offline
trapper
Lugnut  Offline
trapper
L

Joined: Dec 2006
Posts: 20,033
SEPA
Not all baseboards have bleeders. If yours don't you have to bleed and fill at the boiler. I've watched my plumber do it at a few rental units, it's a process.


Eh...wot?

Re: hot water baseboard heat. [Re: pcr2] #6680266
12/01/19 07:57 AM
12/01/19 07:57 AM
Joined: Oct 2017
Posts: 5,878
perry co.Pa
wetdog Offline
trapper
wetdog  Offline
trapper

Joined: Oct 2017
Posts: 5,878
perry co.Pa
Without seeing how it's plumbed it's tough.
Find the bleeder for that zone. Little brass looking thing with a small cap on top.
Flow water to that zone and loosen that little cap
When water comes out the cap stop the water flow
Let it run a bit and repeat. Sometimes you just don't get it all the first time.

Re: hot water baseboard heat. [Re: pcr2] #6680271
12/01/19 08:04 AM
12/01/19 08:04 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
jr.'s cold and sitting here googlin everything.his best friend is the local contractor and they say as soon as they ake up a little they are gonna figure something out.

i think he just wants me to go check traps so he can sleep on the couch in front of the fireplace.

i have to get checkin though cause it aint pretty out and only gettin worse the say.

thanks guys and stay tuned.









Re: hot water baseboard heat. [Re: pcr2] #6680281
12/01/19 08:30 AM
12/01/19 08:30 AM
Joined: Dec 2006
Posts: 20,033
SEPA
L
Lugnut Offline
trapper
Lugnut  Offline
trapper
L

Joined: Dec 2006
Posts: 20,033
SEPA
Looks like you guys are getting some sleet/freezing rain for the next couple of hours at least.


Eh...wot?

Re: hot water baseboard heat. [Re: pcr2] #6680285
12/01/19 08:35 AM
12/01/19 08:35 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
man,i just went to start the stove in my shop and looked like i had the old flinstone mobile in high gear.everything is coated and they say its just startin.told the wife,you can have 400 wheel drive and it wouldn;t do no good.









Re: hot water baseboard heat. [Re: pcr2] #6680301
12/01/19 09:03 AM
12/01/19 09:03 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
feel free to laugh,bathroom is easy access and well lighted so started there.can see step 1 involves a shop vac.but,i look at the bleeder and for no reason i can think of-put the robo grips on it to turn it.fortunately i saw the little screw before i turned anything. crazy









Re: hot water baseboard heat. [Re: pcr2] #6680303
12/01/19 09:15 AM
12/01/19 09:15 AM
Joined: Mar 2014
Posts: 4,369
N.C MO
T
TONY.F Offline
trapper
TONY.F  Offline
trapper
T

Joined: Mar 2014
Posts: 4,369
N.C MO
bleed al your highest elevated radiators first! The last few base board units I bled had bleeders on the opposite end of were the water supply was. All of them ive ever worked on either had a bleeder or a union some were close to each radiator. There should also be a pop off at your boiler for bleeding air. That way is messy but slowly works


LIVE LIFE LIKE THEIR IS NO TOMMORROW
Re: hot water baseboard heat. [Re: pcr2] #6680320
12/01/19 09:31 AM
12/01/19 09:31 AM
Joined: Jun 2018
Posts: 4,764
Beatrice, NE
L
loosegoose Offline
trapper
loosegoose  Offline
trapper
L

Joined: Jun 2018
Posts: 4,764
Beatrice, NE
We have radiators not baseboards, but there's got to be a bleeder of some sort in the system otherwise you'd never be able to fill them up. Depending on if your baseboards are in parallel or series, there may not be a bleeder at every baseboard. Our bleeders look like this....
[Linked Image]
The hardware store sells a little key to open them. There isn't much pressure in a hydronic heat system, should only be like 2 psi at the highest level of your house so it can take a while to get the air out, and sometimes so much air will come out that there's no pressure, and you have to close the bleeder and let pressure build back up.

Re: hot water baseboard heat. [Re: loosegoose] #6680330
12/01/19 09:41 AM
12/01/19 09:41 AM
Joined: Apr 2008
Posts: 3,177
Albany, NY
B
bobsheedy Offline
trapper
bobsheedy  Offline
trapper
B

Joined: Apr 2008
Posts: 3,177
Albany, NY
Originally Posted by loosegoose
.....sometimes so much air will come out that there's no pressure, and you have to close the bleeder and let pressure build back up.


2X

Re: hot water baseboard heat. [Re: pcr2] #6680335
12/01/19 09:43 AM
12/01/19 09:43 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
we are done with number 1 and have it figured out.wife says only 31 more to go and i know she may have missed one.we are at .2 or .3 in of ice since daylight so not much else to do right now.

huge thanks guys.

the bleeder at the boiler is 5 ft from my sons head so i wont diddle with that for a bit but wifes a vaccumin like no tomorrow.told her how much money we were wastin and bein tighter than bark on a tree,she took off like me when i see the bat signal.

house was built in 1980 so most things are fairly modern and new thankfully.wife did take my bfh aay just to be safe though. grin









Re: hot water baseboard heat. [Re: pcr2] #6680337
12/01/19 09:47 AM
12/01/19 09:47 AM
Joined: Dec 2006
Posts: 289
PA
S
scrapper Offline
trapper
scrapper  Offline
trapper
S

Joined: Dec 2006
Posts: 289
PA
If you have an automatic water feed, make sure it is working before bleeding to much. The system should have 12 pounds when cold. There is a chance that it could be the pump too. Getting weak and not pushing the water well enough.

Re: hot water baseboard heat. [Re: pcr2] #6680352
12/01/19 10:06 AM
12/01/19 10:06 AM
Joined: Dec 2006
Posts: 1,117
Adirondacks, N.Y.
T
trapdye Offline
trapper
trapdye  Offline
trapper
T

Joined: Dec 2006
Posts: 1,117
Adirondacks, N.Y.
Would the expansion tank have anything to do with slow flow ?


John's Nuisance Wildlife Control
If you like what you do for a living, It's better than a vacation. Most days.
Re: hot water baseboard heat. [Re: pcr2] #6680367
12/01/19 10:19 AM
12/01/19 10:19 AM
Joined: Sep 2019
Posts: 35
Mo.
J
JimEvans Offline
trapper
JimEvans  Offline
trapper
J

Joined: Sep 2019
Posts: 35
Mo.
Would the expansion tank have anything to do with slow flow ?

Only if it is water logged/ Full of water.
It should be just over 1/2 full of water.

Just take your time and bleed the air out one unit at a time.
Things will warm up but remember as you remove the air it is being replaced with cold water at the furnace, so don't rush it.
You most likely will have to do them 2 or 3 times before removing all of the air.

Good luck


Jim Evans
Re: hot water baseboard heat. [Re: pcr2] #6680369
12/01/19 10:21 AM
12/01/19 10:21 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
thanks guys.imagine its been a while for the whole works.









Re: hot water baseboard heat. [Re: pcr2] #6680386
12/01/19 10:51 AM
12/01/19 10:51 AM
Joined: Dec 2015
Posts: 1,028
West Cent IL
illinideer Offline
trapper
illinideer  Offline
trapper

Joined: Dec 2015
Posts: 1,028
West Cent IL
I had to bleed mine a few times to get the air out. I installed a new boiler and relocated a base board register for a kitchen remodel. As for a bad expansion tank I dont believe it will hurt water flow. The bladder was bad in mine and when the boiler got the water up to temp it would dribble out of the boiler pop off safety valve cause the expanding water had no place to go. My cold pres is 12 psi and up to temp 23-24 psi.

Last edited by illinideer; 12/01/19 10:53 AM.



Coyote 5 Badger 1
Coons 17
Bobcats 2 Released
Grinners All of them
USN AE2 VF-31 Tomcatters
Retired SMSGT IL ANG 183 Fighter Wing
Coyote U Class #4
Re: hot water baseboard heat. [Re: pcr2] #6680391
12/01/19 10:58 AM
12/01/19 10:58 AM
Joined: May 2010
Posts: 28,978
potter co. p.a.
P
pcr2 Offline OP
"Twerker"
pcr2  Offline OP
"Twerker"
P

Joined: May 2010
Posts: 28,978
potter co. p.a.
i get that little stream like when youre takin a leek and think your done but nope-not quite-outta each one.