pole barn radiant heat or not #6986850
09/10/20 12:14 AM
09/10/20 12:14 AM
Joined: Nov 2009
Posts: 843
upstate NY
M
Mr. Ed Offline OP
trapper
Mr. Ed  Offline OP
trapper
M

Joined: Nov 2009
Posts: 843
upstate NY
Going to be building a 40x72 pole barn. The floor with be poured concrete with 2" foam board . Was thinking of adding radiant heat since it will be a workshop/storage. I will have a propane heater in a workshop area kept at about 50 degrees and fire up a woodstove to add some heat while working. Anybody wished they added radiant heat after a pour ? I have not looked into pricing but was thinking of putting in a lift and was a little worried about hitting a tubing run down the road if I did do it.

Re: pole barn radiant heat or not [Re: Mr. Ed] #6986864
09/10/20 12:29 AM
09/10/20 12:29 AM
Joined: Sep 2013
Posts: 18,533
Green County Wisconsin
G
GREENCOUNTYPETE Offline
trapper
GREENCOUNTYPETE  Offline
trapper
G

Joined: Sep 2013
Posts: 18,533
Green County Wisconsin
my uncle did the radiant heat it is nice , quiet , doesn't blow around dust , raise the 14 foot door pull in a truck or tractor and close the door in 5 minutes back to normal temp.

the cost to put in some tubing is minimal compared to the concrete cost

4 post lift or 2 post lift

2 post require more than just a basic concrete floor you want a 10 inch deep 4x4 foot pad for each post typically if you spec out the lift and pour the pad for the lift with no tubing for the heat in it then pour the rest of the floor around it with tubing no worries about hitting the tubing


America only has one issue, we have a Responsibility crisis and everything else stems from it.
Re: pole barn radiant heat or not [Re: Mr. Ed] #6986907
09/10/20 05:20 AM
09/10/20 05:20 AM
Joined: Jun 2016
Posts: 14,105
Michigan
T
Trapper Dahlgren Online content
trapper
Trapper Dahlgren  Online Content
trapper
T

Joined: Jun 2016
Posts: 14,105
Michigan
in floor heat is nice had it in a building , do what Pete said , I would , if you have a good source wood , put a boiler in

Re: pole barn radiant heat or not [Re: Mr. Ed] #6986978
09/10/20 07:29 AM
09/10/20 07:29 AM
Joined: Jan 2015
Posts: 3,446
Houghton Lake, MI
strike2x Offline
trapper
strike2x  Offline
trapper

Joined: Jan 2015
Posts: 3,446
Houghton Lake, MI
I built a 60x 100 for my nephew's salvage yard. In floor heat throughout. It is awesome. He has 2 lifts. Just plan for them and tube around area. Make a map of tube for future reference. We put all the tube in. He has propane boiler that also runs water heater. You can buy all the tube online for cheaper than anywhere. Bring all tube ends up in pairs so whoever install boiler can put them into a manifold. I think 250 foot was recommended longest run. Even if yo don't put boiler in right away the tubes are in. We saved about $5000 by putting in out own tubes. There is a lot of information on the internet to guide you.


Wish I had more time to trap....
Re: pole barn radiant heat or not [Re: Mr. Ed] #6987020
09/10/20 08:23 AM
09/10/20 08:23 AM
Joined: Mar 2013
Posts: 799
MN
O
oneeyedtrapper Offline
trapper
oneeyedtrapper  Offline
trapper
O

Joined: Mar 2013
Posts: 799
MN
IMO, it's the only way to go!

Re: pole barn radiant heat or not [Re: Mr. Ed] #6987035
09/10/20 08:41 AM
09/10/20 08:41 AM
Joined: Dec 2012
Posts: 6,523
Wi.
D
Diggerman Offline
trapper
Diggerman  Offline
trapper
D

Joined: Dec 2012
Posts: 6,523
Wi.
Yes, take detailed pics of tube placement.

Re: pole barn radiant heat or not [Re: Mr. Ed] #6987115
09/10/20 10:34 AM
09/10/20 10:34 AM
Joined: Dec 2007
Posts: 1,513
Kanabec Cty, MN
D
Drakej Offline
trapper
Drakej  Offline
trapper
D

Joined: Dec 2007
Posts: 1,513
Kanabec Cty, MN
Documentation of pex tube runs is a very good practice BUT if it didn't get done or lost or in doubt the runs are clearly visible with even an economy thermal scanner while they are running heat. Space your pex closer around exterior walls as this is where your heat will be lost the fastest. Pex is being spaced as close as 6" often now. It take more and means more loops but it give quicker response time to heat floor(if that is wanted). Smaller independent space heater can do the same if you want to keep space above freezing and warm up just for projects time to time. Take advantage of any solar exposure opportunity you might have, passive or active. That thermal mass in your floor can store FREE solar heat as well as it does with the hot water you run thru it if you need it. I'm not in the best solar area but we still get better than 50% of our heat from solar thru a heating season.


I've learned enough thru the years to now know that I don't know enough. KNOWLEDGE IS FREEDOM.
Re: pole barn radiant heat or not [Re: Mr. Ed] #6989117
09/13/20 01:11 AM
09/13/20 01:11 AM
Joined: Nov 2009
Posts: 843
upstate NY
M
Mr. Ed Offline OP
trapper
Mr. Ed  Offline OP
trapper
M

Joined: Nov 2009
Posts: 843
upstate NY
I am going to look into internet pricing on the pex tubing.