ROOF LEAK ON NEW METAL ROOF #7188072
02/18/21 03:57 PM
02/18/21 03:57 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
OMG!!, NOT AGAIN!!!!!!!!! mad


Had the new metal roof installed over the old low sloop flat roof, Replaced the forced hot air gas furnace with a hot water gas fired Boiler. Everything was running fine last Winter. At 1:30 AM this Morning, I was in the Bathroom, and thought I heard the Toilet leaking. No leak on the Toilet. Then, I looked at the window sill. Water was dripping off the Window sill. I looked at the wall to the right of the Window. 3 lines of WATER RUNNING DOWN THE WALL FROM THE BATHROOM CEILING!! mad I go upstairs this Morning, and checked the walls in the Bedrooms and the Bathroom. No leaks or wetness so, far. I knocked some icicles off of the over hang around the gutters and noticed some ice in the vents on the overhang of the new metal roof. Knocked those off, Had the upstairs boiler set at 65. So I don't see how that could cause heat loss. Turned it down to 56 Degrees..

Called Contractor that installed the new Metal roof twice this Morning. Never returned calls.

Any suggestions on what is now causing this leak and ice build up ? 14 inches of blown in insulation in the attic..

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188077
02/18/21 03:59 PM
02/18/21 03:59 PM
Joined: Oct 2009
Posts: 6,407
east central WI
K
k snow Offline
trapper
k snow  Offline
trapper
K

Joined: Oct 2009
Posts: 6,407
east central WI
What's the slop on the metal now? Nobody around here will install steel less than 4:12 pitch.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188083
02/18/21 04:02 PM
02/18/21 04:02 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
It was 3:12 before, they added some boards to increase the slope; when they installed the Metal roof.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188086
02/18/21 04:04 PM
02/18/21 04:04 PM
Joined: Feb 2009
Posts: 828
Hill City,Mn.
R
Rally Offline
trapper
Rally  Offline
trapper
R

Joined: Feb 2009
Posts: 828
Hill City,Mn.
Sounds like a condensation build up from frozen vents or sewer vent. maybe gutters freezing and backing up in soffets. I'd be in the attic checking out vent fan ducting and such first, then any pipes/chimneys that go through the roof.


Keep your boots dry
Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188093
02/18/21 04:05 PM
02/18/21 04:05 PM
Joined: Dec 2009
Posts: 20,331
The Hill Country of Texas
Leftlane Offline
"HOSS"
Leftlane  Offline
"HOSS"

Joined: Dec 2009
Posts: 20,331
The Hill Country of Texas
Man I feel bad for you.

Metal roofs never leak- ever. The fasteners, flashings, and valleys almost always leak and it is an installer issue or a problem matching the correct materials to your needs. B4 yall spend money on metal hit me up for my do's and don'ts. Roofers who have been doing it for years mean they screwed it down and the check cashed. I am the hard (This word is unacceptable on Trapperman) that gets called when the muffed it and they to it at least 50% of the time


“What’s good for me may not be good for the weak minded.”
Captain Gus McCrae- Texas Rangers


Re: ROOF LEAK ON NEW METAL ROOF [Re: Rally] #7188120
02/18/21 04:23 PM
02/18/21 04:23 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
Originally Posted by Rally
Sounds like a condensation build up from frozen vents or sewer vent. maybe gutters freezing and backing up in soffets. I'd be in the attic checking out vent fan ducting and such first, then any pipes/chimneys that go through the roof.



Only vent, would be the vent for the toilets. Got a Septic system. That is working great. No power vent fans. There are roof vents on the regular shingle part of the roof on the front part of the house.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188146
02/18/21 04:34 PM
02/18/21 04:34 PM
Joined: Mar 2007
Posts: 35,169
McGrath, AK
W
white17 Offline

"General (Mr.Sunshine) Washington"
white17  Offline

"General (Mr.Sunshine) Washington"
W

Joined: Mar 2007
Posts: 35,169
McGrath, AK
If you have water downstairs but not upstairs, I think I'd be suspecting a waterline leaking in the first floor ceiling. You are not going to have a roof leak that avoids the second story and shows up on the first floor.

Be sure to check around ceiling light fixtures for standing water


Mean As Nails
Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188172
02/18/21 04:46 PM
02/18/21 04:46 PM
Joined: Jan 2012
Posts: 1,316
PA
P
panaxman Offline
trapper
panaxman  Offline
trapper
P

Joined: Jan 2012
Posts: 1,316
PA
Show us some pix. You may have ice dams packed way up your roof. Your contractor should at least stop out and take a look. Here in SE PA we have been dealing with numerous leaks due to ice dams. I go out immediately to past customers and inspect the leak and try to help. Drive over the contractor's place and show him pix, let him have a chance at making it right.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188192
02/18/21 04:56 PM
02/18/21 04:56 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
[Linked Image]

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188193
02/18/21 04:57 PM
02/18/21 04:57 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
leak from ceiling down along the wall in the 1st floor Bathroom

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188197
02/18/21 04:59 PM
02/18/21 04:59 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
[Linked Image]


Water running down the bathroom wall

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188201
02/18/21 05:03 PM
02/18/21 05:03 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
[Linked Image]


Plasterboard bubbling out in the middle of the 2nd floor bedroom to the left of the 2nd floor bathroom

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188207
02/18/21 05:05 PM
02/18/21 05:05 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
[Linked Image]


Ice around vents on the overhang of the roof.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188218
02/18/21 05:11 PM
02/18/21 05:11 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
Originally Posted by white17
If you have water downstairs but not upstairs, I think I'd be suspecting a waterline leaking in the first floor ceiling. You are not going to have a roof leak that avoids the second story and shows up on the first floor.

Be sure to check around ceiling light fixtures for standing water



This new leak happened in the exact same spot as the old leak, which was the reason for replacing the heating system and putting the metal roof on.. Checked the lights , toilet up stairs, sinks. no leaks.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188227
02/18/21 05:17 PM
02/18/21 05:17 PM
Joined: Jan 2012
Posts: 1,316
PA
P
panaxman Offline
trapper
panaxman  Offline
trapper
P

Joined: Jan 2012
Posts: 1,316
PA
Yep, ice dams. How is the low slope metal roof tied into the main house wall? perhaps ice water is packed up over the flashing. If you can, use a shop broom or plastic shovel and get as much snow off. Drill a hole in the ceiling and let the water drain out into a bucket. I saw a guy's ceiling come down 'cause the water kept accumulating without a drain hole.

After the meltdown, pick up some gutter heater wires and keep the gutters from freezing. I think that is the culprit.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188228
02/18/21 05:18 PM
02/18/21 05:18 PM
Joined: Mar 2007
Posts: 35,169
McGrath, AK
W
white17 Offline

"General (Mr.Sunshine) Washington"
white17  Offline

"General (Mr.Sunshine) Washington"
W

Joined: Mar 2007
Posts: 35,169
McGrath, AK
But you DO have water on the upstairs walls ?? If your heating system penetrates the roof, you could have an ice dam down slope of that penetration. Water backing up and running into incorrectly flashed exhaust

Agree it could also be the gutters. Don't wait around to get it checked. You don't want the ceiling coming down


Mean As Nails
Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188246
02/18/21 05:30 PM
02/18/21 05:30 PM
Joined: Mar 2018
Posts: 948
Indiana
H
Huntall76 Offline
trapper
Huntall76  Offline
trapper
H

Joined: Mar 2018
Posts: 948
Indiana
This is a guess but an educated one. This can happen to any roof in the right circumstance. When snow melts and freezes and then starts to melt again if it's still frozen at the bottom edge of your roof but the upper part of your roof starts to melt the water will back up and will find a way in. There are only (2) ways that I know of to stop this on a roof (1st) is to silicone the overlap on the metal sheets (preferably as they are put on). I put a metal roof on my old camper that has 2:12 maybe 3:12 pitch and have never had a leak. (2nd) is if you use those heating elements that you string across your roof and down your gutter. I know this can happen even on high pitch roofs. My old boss had this problem because he has skylights that would allow the peak of the roof to melt while the bottom was still frozen. He used option (2). I'm not positive if this is your problem but it sounds like it. Good luck.

Re: ROOF LEAK ON NEW METAL ROOF [Re: white17] #7188249
02/18/21 05:32 PM
02/18/21 05:32 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
No water on the upstairs, yet. The Gas fired hot water boiler vents directly to the outside side wall. . That boiler is in the furnace room that is next to the upstairs bedroom.

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188252
02/18/21 05:34 PM
02/18/21 05:34 PM
Joined: Oct 2017
Posts: 5,878
perry co.Pa
wetdog Offline
trapper
wetdog  Offline
trapper

Joined: Oct 2017
Posts: 5,878
perry co.Pa
Gutter backed up or metal could be lapped the wrong way.
Seen both a time or two. Lol

Re: ROOF LEAK ON NEW METAL ROOF [Re: Canvasback2] #7188271
02/18/21 05:44 PM
02/18/21 05:44 PM
Joined: Mar 2007
Posts: 35,169
McGrath, AK
W
white17 Offline

"General (Mr.Sunshine) Washington"
white17  Offline

"General (Mr.Sunshine) Washington"
W

Joined: Mar 2007
Posts: 35,169
McGrath, AK
Yes lapped the wrong direction could be an issue too but you obviously have water coming from somewhere


Originally Posted by Canvasback2
[Linked Image]


Plasterboard bubbling out in the middle of the 2nd floor bedroom to the left of the 2nd floor bathroom



If this is on the second floor why do you say ...."no water upstairs yet" ?????????????