Electrical question.
#6299397
08/11/18 06:01 PM
08/11/18 06:01 PM
|
Joined: Mar 2013
Posts: 17,044 Fredonia, PA.
Finster
OP
trapper
|
OP
trapper
Joined: Mar 2013
Posts: 17,044
Fredonia, PA.
|
My RV is 30 amp. I bought a 50 foot extension cord for it. I'm not sure what gauge it is, probably cheap China crap. Trouble is that it won't carry enough amps to run the AC it will just make the compressor hum. (AC unit is fine) I'm going to buy another cord. Should a 10 gauge cord be robust enough to run the AC with a 50ft length?
I BELIEVE IN MY GOD, MY COUNTRY AND IN MYSELF.
|
|
|
Re: Electrical question.
[Re: Finster]
#6299406
08/11/18 06:11 PM
08/11/18 06:11 PM
|
Joined: Jun 2007
Posts: 16,150 Tennessee
Scuba1
"color blind Kraut"
|
"color blind Kraut"
Joined: Jun 2007
Posts: 16,150
Tennessee
|
Where is the other end of that chord plugged into? But yes you should not have much of a voltage drop in a 10wg 50 foot chord if the supply is up to snuff.
Let's go Brandon
"Shall not comply" with morons who don't understand "shall not infringe."
|
|
|
Re: Electrical question.
[Re: Finster]
#6299408
08/11/18 06:13 PM
08/11/18 06:13 PM
|
Joined: Dec 2011
Posts: 10,430 MT
snowy
trapper
|
trapper
Joined: Dec 2011
Posts: 10,430
MT
|
Yes you will be fine with #10 AWG for both 120V or 240V for the distance of 50 ft. and for a 30 amp service it will also have a VD of 3%. You should be good to go with #10 AWG.
I might add at the distant of 60 with the same other constants you would want to go with #8 AWG.
Last edited by snowy; 08/11/18 06:19 PM.
Give me a fish, I will eat for a day. Teach me to fish, I will eat for a lifetime
|
|
|
Re: Electrical question.
[Re: Finster]
#6299427
08/11/18 06:46 PM
08/11/18 06:46 PM
|
Joined: Mar 2013
Posts: 17,044 Fredonia, PA.
Finster
OP
trapper
|
OP
trapper
Joined: Mar 2013
Posts: 17,044
Fredonia, PA.
|
I have it plugged into an outlet that was for my welder. I just converted it to a 30 amp plug and made one of the hots a common in the panel. If I remember correctly, I have 10 gauge 3 wire to the outlet. Probably a good 50 feet on a 50 amp breaker. So the extension cord would be another 50 feet off of that.
I BELIEVE IN MY GOD, MY COUNTRY AND IN MYSELF.
|
|
|
Re: Electrical question.
[Re: Finster]
#6299438
08/11/18 07:15 PM
08/11/18 07:15 PM
|
Joined: Jan 2012
Posts: 3,051 Ohio
OhioBoy
trapper
|
trapper
Joined: Jan 2012
Posts: 3,051
Ohio
|
|
|
|
Re: Electrical question.
[Re: Finster]
#6299450
08/11/18 07:45 PM
08/11/18 07:45 PM
|
Joined: Dec 2006
Posts: 20,100 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 20,100
SEPA
|
10 gauge copper is rated 30 amps.
Eh...wot?
|
|
|
Re: Electrical question.
[Re: Finster]
#6299519
08/11/18 09:29 PM
08/11/18 09:29 PM
|
Joined: Jun 2007
Posts: 16,150 Tennessee
Scuba1
"color blind Kraut"
|
"color blind Kraut"
Joined: Jun 2007
Posts: 16,150
Tennessee
|
And you are sure that the start capacitor on the AC units compressor is ok ?
Let's go Brandon
"Shall not comply" with morons who don't understand "shall not infringe."
|
|
|
Re: Electrical question.
[Re: Scuba1]
#6299526
08/11/18 09:35 PM
08/11/18 09:35 PM
|
Joined: Mar 2013
Posts: 17,044 Fredonia, PA.
Finster
OP
trapper
|
OP
trapper
Joined: Mar 2013
Posts: 17,044
Fredonia, PA.
|
And you are sure that the start capacitor on the AC units compressor is ok ? Yup, works fine when connected directly to the outlet or generator. It's defiantly the extension cord.
I BELIEVE IN MY GOD, MY COUNTRY AND IN MYSELF.
|
|
|
Re: Electrical question.
[Re: Finster]
#6299791
08/12/18 09:49 AM
08/12/18 09:49 AM
|
Joined: Feb 2007
Posts: 2,632 Ohio, 55yrs old
Pasadena
trapper
|
trapper
Joined: Feb 2007
Posts: 2,632
Ohio, 55yrs old
|
I have it plugged into an outlet that was for my welder. I just converted it to a 30 amp plug and made one of the hots a common in the panel. If I remember correctly, I have 10 gauge 3 wire to the outlet. Probably a good 50 feet on a 50 amp breaker. So the extension cord would be another 50 feet off of that. As was said above, the 10awg is good for 30amps. So you are really running 100’ on that #10. I bet when you were running that welder that #10 was heating up at the breaker though. You are by code pushing the limits on the #10. Having it on the 50amp breaker is a big no-no. I’m wondering what the actual load the ac is drawing though.
|
|
|
Re: Electrical question.
[Re: Finster]
#6299867
08/12/18 11:52 AM
08/12/18 11:52 AM
|
Joined: Dec 2010
Posts: 11,217 Armpit, ak
Dirt
trapper
|
trapper
Joined: Dec 2010
Posts: 11,217
Armpit, ak
|
Voltage drop,as has been mentioned,is your problem. Electric motors are very voltage sensitive. The start up current can be 3 times the running current. Voltage drop is a function of current and resistance. Smaller wire and greater distance means more resistance equals more voltage drop.
P.s. overrated cheap generators will have smaller wire windings and can have substantial voltage drop at the generator when operated near the rated watts.
Last edited by Dirt; 08/12/18 12:01 PM.
Who is John Galt?
|
|
|
Re: Electrical question.
[Re: jbyrd63]
#6300083
08/12/18 05:06 PM
08/12/18 05:06 PM
|
Joined: Mar 2013
Posts: 17,044 Fredonia, PA.
Finster
OP
trapper
|
OP
trapper
Joined: Mar 2013
Posts: 17,044
Fredonia, PA.
|
Just go to an electric supply house and get a piece of S O cord #8 . Put the plugs on each end. Don't have to worry about it . Plus for what you spend you won't leave it behind. BUT if you keep trying to start your AC on low voltage you will be replacing it soon and often !!!! Cheaper to get the right cord. Probably what I'm going to do. I can get 50' of that for around $100 and put some 30amp plug ends on it. I'll put regular plug ends on the one I have now and use it for a regular outlet 20 amp for saws and such.
Last edited by Finster; 08/12/18 05:06 PM.
I BELIEVE IN MY GOD, MY COUNTRY AND IN MYSELF.
|
|
|
Re: Electrical question.
[Re: Finster]
#6300089
08/12/18 05:13 PM
08/12/18 05:13 PM
|
Joined: Dec 2006
Posts: 21,081 St. Louis Co, Mo
BigBob
trapper
|
trapper
Joined: Dec 2006
Posts: 21,081
St. Louis Co, Mo
|
You keep talking Amps, but didn't answer the question of is it 110 or 220 VOLTS?
Every kid needs a Dog and a Curmudgeon.
Remember Bowe Bergdahl, the traitor.
Beware! Jill Pudlewski, Ron Oates and Keven Begesse are liars and thiefs!
|
|
|
Re: Electrical question.
[Re: BigBob]
#6300103
08/12/18 05:33 PM
08/12/18 05:33 PM
|
Joined: Mar 2013
Posts: 17,044 Fredonia, PA.
Finster
OP
trapper
|
OP
trapper
Joined: Mar 2013
Posts: 17,044
Fredonia, PA.
|
You keep talking Amps, but didn't answer the question of is it 110 or 220 VOLTS? It's on an RV. 120 volt the entire RV is 30 amp.