Re: New furnace is junk.
[Re: 1lessdog]
#8051289
01/16/24 11:17 AM
01/16/24 11:17 AM
|
Joined: Mar 2018
Posts: 2,238 Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Posts: 2,238
Missouri
|
Was old boiler hot water or steam? Old steam boilers were magical instruments.
Last edited by HayDay; 01/16/24 11:17 AM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051291
01/16/24 11:20 AM
01/16/24 11:20 AM
|
Joined: Aug 2008
Posts: 16,291 ny
upstateNY
trapper
|
trapper
Joined: Aug 2008
Posts: 16,291
ny
|
Make them upgrade to what you need.
the wheels of the gods turn very slowly
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051314
01/16/24 11:44 AM
01/16/24 11:44 AM
|
Joined: Oct 2009
Posts: 7,429 western mn
bucksnbears
trapper
|
trapper
Joined: Oct 2009
Posts: 7,429
western mn
|
This sucks but I've been hearing of similar problems the past few years.
swampgas chili and schmidt beer makes for a deadly combo
You have to remember that 1 out of 3 Democratic Voters is just as dumb as the other two.
|
|
|
Re: New furnace is junk.
[Re: HayDay]
#8051331
01/16/24 11:58 AM
01/16/24 11:58 AM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Was old boiler hot water or steam? Old steam boilers were magical instruments. Hot water, we have the baseboards. Not the big cast iron heaters.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051361
01/16/24 12:25 PM
01/16/24 12:25 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Not a heating guy. Just have an oil fired boiler and baseboard heat, so is the boiler running all the time? If so the boiler is too small in my opinion.
Back in time when we got weeks of -50f my boiler would run a lot but not constantly.
Last edited by Oh Snap; 01/16/24 12:33 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051378
01/16/24 12:40 PM
01/16/24 12:40 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
I cant find a BTU rating for old boiler. The heating guy says the new boiler is running at 25 percent. I said if that true were only using 27000 BTU's to heat the house. The pipes coming up to and going out of baseboards are hot and the fins are luke warm. They have tried both speeding up the pump and slowing it down. The set temp is at 180 degree F. I have never seen it get to top temp. Its normally running at 165 to 175F
Last edited by 1lessdog; 01/16/24 12:41 PM.
|
|
|
Re: New furnace is junk.
[Re: HayDay]
#8051381
01/16/24 12:41 PM
01/16/24 12:41 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
There is a canister on the floor to bleed off any air in the system. There is only one pump and 3 zones. All 3 have there own thermostat.
The guy last night said we could get a regular hot water heater and use it to keep heated water in and circulate . I dont know if thats is possible.
Last edited by 1lessdog; 01/16/24 12:48 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051390
01/16/24 12:47 PM
01/16/24 12:47 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
The second opinion you received was too small boiler and that was it or did he try to get the boiler up to working correctly. Seems to me that there is a problem with the burner controls. Is there any burner tune up guys there that you can get advice from?
Auto bleeder or manual?
Glycol or water?
Last edited by Oh Snap; 01/16/24 12:50 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051398
01/16/24 12:53 PM
01/16/24 12:53 PM
|
Joined: Aug 2008
Posts: 16,291 ny
upstateNY
trapper
|
trapper
Joined: Aug 2008
Posts: 16,291
ny
|
Get the idiots that installed the thing to make it right.Mess around with it on your own and they will say you voided any warrenty.
the wheels of the gods turn very slowly
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051405
01/16/24 12:56 PM
01/16/24 12:56 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
You shouldn't have to do all this checking. BUT go to NAPA and purchase an inferred temperature reader and know the actual temperature it would help to know beyond feeling the pipes. They aren't expensive. The bleeder might be automatic and not working and there could be an air lock. But the boiler not reaching operating temperature is a clue to the problem if I understand correctly..
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: upstateNY]
#8051406
01/16/24 12:59 PM
01/16/24 12:59 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Get the idiots that installed the thing to make it right.Mess around with it on your own and they will say you voided any warrenty. Your right but they can't so he had to come to the Ex-Sperts.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: Oh Snap]
#8051414
01/16/24 01:07 PM
01/16/24 01:07 PM
|
Joined: Aug 2008
Posts: 16,291 ny
upstateNY
trapper
|
trapper
Joined: Aug 2008
Posts: 16,291
ny
|
Get the idiots that installed the thing to make it right.Mess around with it on your own and they will say you voided any warrenty. Your right but they can't That's when its time to call consumer affairs and the better business bureau.It their job to take care of stuff like this.
the wheels of the gods turn very slowly
|
|
|
Re: New furnace is junk.
[Re: Oh Snap]
#8051541
01/16/24 02:56 PM
01/16/24 02:56 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
The second opinion you received was too small boiler and that was it or did he try to get the boiler up to working correctly. Seems to me that there is a problem with the burner controls. Is there any burner tune up guys there that you can get advice from?
Auto bleeder or manual?
Glycol or water? Auto bleeder Glycol
|
|
|
Re: New furnace is junk.
[Re: white17]
#8051542
01/16/24 02:57 PM
01/16/24 02:57 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Have you checked your fuel consumption ? Do you know how much you started with ? Is the boiler getting enough fuel ? Is there a restriction in the line or a filter that is clogged ? Are you burning #1 fuel oil ? I, as others, suspect the unit is undersized if everything is functioning as it should. Were on are 3rd tank of Propane 500 gallon They increased gas pressure
Last edited by 1lessdog; 01/16/24 02:58 PM.
|
|
|
Re: New furnace is junk.
[Re: upstateNY]
#8051551
01/16/24 03:04 PM
01/16/24 03:04 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Get the idiots that installed the thing to make it right.Mess around with it on your own and they will say you voided any warrenty. I have not touched it. When they unhooked the old boiler they also unhooked the Electric boiler and that does not work now. We were getting dual fuel rate from the power company.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051572
01/16/24 03:23 PM
01/16/24 03:23 PM
|
Joined: Mar 2007
Posts: 35,179 McGrath, AK
white17
"General (Mr.Sunshine) Washington"
|
"General (Mr.Sunshine) Washington"
Joined: Mar 2007
Posts: 35,179
McGrath, AK
|
Have you checked your fuel consumption ? Do you know how much you started with ? Is the boiler getting enough fuel ? Is there a restriction in the line or a filter that is clogged ? Are you burning #1 fuel oil ? I, as others, suspect the unit is undersized if everything is functioning as it should. Were on are 3rd tank of Propane 500 gallon They increased gas pressure Oh. Propane ! Maybe it is getting too cold for the propane to get from the tank to the furnace. What kind of temperatures are you getting ? I'm sure there is no wind there either !!
Mean As Nails
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051573
01/16/24 03:26 PM
01/16/24 03:26 PM
|
Joined: Aug 2008
Posts: 16,291 ny
upstateNY
trapper
|
trapper
Joined: Aug 2008
Posts: 16,291
ny
|
Get the idiots that installed the thing to make it right.Mess around with it on your own and they will say you voided any warrenty. I have not touched it. When they unhooked the old boiler they also unhooked the Electric boiler and that does not work now. We were getting dual fuel rate from the power company. Well,,take my advice in my previous posts .
the wheels of the gods turn very slowly
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051574
01/16/24 03:29 PM
01/16/24 03:29 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
You originally had an oil boiler. Sorry for thinking that's what you put back in.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051576
01/16/24 03:31 PM
01/16/24 03:31 PM
|
Joined: Dec 2006
Posts: 9,709 ND
MJM
trapper
|
trapper
Joined: Dec 2006
Posts: 9,709
ND
|
Be glad you were not up here by me. I would guess I averaged 5-10 degrees colder than you did. I had 20 below this morning, so it is warming up.
"Not Really, Not Really" Mark J Monti "MJM you're a jerk."
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051605
01/16/24 04:28 PM
01/16/24 04:28 PM
|
Joined: Mar 2018
Posts: 2,238 Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Posts: 2,238
Missouri
|
The large system I worked with had 4 zones and 4 pumps. When the thermostat called for heat, the pump kicked on. Took me a while to wrap my head around it, but these were suction pumps in the basement of a 3 story building. Hot water would rise on supply side, cold water would sink on return, so pumps basically just boosted the natural thermo syphon to keep hot water running in the loop. But for that to work, could be no air in system to break the syphon or sediment in system to impede the flow.
Baseboards we had were just a piece of fin tube. Same diameter supply pipe soldered to end of the fin tube pipe. Hot water flowed thru and fins radiated heat. Don't understand how water could be hot on either side and not the tube in the middle, unless water is only conducting heat and not flowing.
The complete loop starting from boiler reservoir / supply was then loop up, then at very peak of the loop was a riser with a ball check valve on it. Any air in the loop would float up to the riser and vent.......then once purged, water pressure would hold the ball check valve closed. It was self venting. Loop would complete back to pump and cycle continued. Also required was a source of makeup water to keep the system filled with slight pressure to hold check valves closed and in the basement an expansion tank filled with captive air to act as a shock absorber.The ball check valves got most of the air trapped in the system, but there were manual bleeder valves too. If loop wasn't flowing had to check them all. An air lock would shut down the flow and you got nothing.
So if you have three loops and one pump, how does the thermostat call for heat? What happens when it does? Does an electric solenoid type valve open and close?
Last edited by HayDay; 01/16/24 05:27 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051625
01/16/24 04:43 PM
01/16/24 04:43 PM
|
Joined: Mar 2014
Posts: 1,325 vermont
vermontster
trapper
|
trapper
Joined: Mar 2014
Posts: 1,325
vermont
|
Try turning down one of the zones so it’s not calling for heat and see if that helps heat up the other zones.
The bitterness of poor quality last a lot longer than the sweetness of low price
|
|
|
Re: New furnace is junk.
[Re: vermontster]
#8051637
01/16/24 05:05 PM
01/16/24 05:05 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Try turning down one of the zones so it’s not calling for heat and see if that helps heat up the other zones. I just got home, I will turn 2 of the thermostat down to 50 degrees and leave the one in sleeping level at 70.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051640
01/16/24 05:08 PM
01/16/24 05:08 PM
|
Joined: Dec 2006
Posts: 20,096 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 20,096
SEPA
|
I'm sure that new set up cost a pretty penny. HVAC stuff is stupid expensive.
It stinks that you're having all this trouble. I hope you get it worked out to your satisfaction and keep us updated.
Eh...wot?
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051805
01/16/24 07:53 PM
01/16/24 07:53 PM
|
Joined: Sep 2010
Posts: 6,607 NC, Orange Co.
QuietButDeadly
trapper
|
trapper
Joined: Sep 2010
Posts: 6,607
NC, Orange Co.
|
With multiple zones and a single pump, you are bound to have solenoid valves to control the flow in each zone. Sounds like you have a circulation problem. Either air in the system, solenoids not opening or the pump just not pumping.
We had an oil fired unit with the finned type baseboard exchangers. We had two zones and two pumps. Dad chose that system when the house was built because he did not want forced air that would stir up dust.
I remodeled the house in the 80s and ripped the heating system out and replaced it with a geo thermal heat pump, forced air.
Life Member: NCTA, VTA, NTA, TTFHA, MFTI Member: FTA NRA NWTF
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051844
01/16/24 08:25 PM
01/16/24 08:25 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
I turned 3 thermostat down to 50, to see if the temp will go up on are bedroom. It's been 2 hrs and the room is still at 60. Did not help at all.
The computer board on boiler says the pump is running at 6 gallons per minute. The pump and pipes are so hot you can't put your hands on them. I have said all along is the pump working or is it running the wrong direction.
The guys that put it in says pump is working and running the right direction.
Then why is it 59 or 60 degrees in here.
Last edited by 1lessdog; 01/16/24 08:29 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051857
01/16/24 08:36 PM
01/16/24 08:36 PM
|
Joined: Sep 2010
Posts: 6,607 NC, Orange Co.
QuietButDeadly
trapper
|
trapper
Joined: Sep 2010
Posts: 6,607
NC, Orange Co.
|
Sounds like it is not circulating the hot water.
Your installer should be at your house figuring out what they have plumbed or wired wrong.
Life Member: NCTA, VTA, NTA, TTFHA, MFTI Member: FTA NRA NWTF
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051858
01/16/24 08:36 PM
01/16/24 08:36 PM
|
Joined: Apr 2012
Posts: 2,973 new york
mike mason
trapper
|
trapper
Joined: Apr 2012
Posts: 2,973
new york
|
I turned 3 thermostat down to 50, to see if the temp will go up on are bedroom. It's been 2 hrs and the room is still at 60. Did not help at all.
The computer board on boiler says the pump is running at 6 gallons per minute. The pump and pipes are so hot you can't put your hands on them. I have said all along is the pump working or is it running the wrong direction.
The guys that put it in says pump is working and running the right direction.
Then why is it 59 or 60 degrees in here. Sounds like you have air in the system with the pump/pipes too hot but heat not getting where it is needed. can you bleed the system one zone at a time?
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051864
01/16/24 08:45 PM
01/16/24 08:45 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
The company is All Season Mechanical out of Fargo N.D.
I think the heat I feel in the pipes is conducted heat not pumped heat. The old boil had a issue real similar. The relay to turn the pump on went bad one night. I opened the electric box and wired in a extention cord and let it run all the time and we had heat again.
Last edited by 1lessdog; 01/16/24 08:50 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051871
01/16/24 08:48 PM
01/16/24 08:48 PM
|
Joined: Jan 2012
Posts: 1,639 Warren co Mo
hrdtoflw
trapper
|
trapper
Joined: Jan 2012
Posts: 1,639
Warren co Mo
|
Could they have not opened all valves properly. I have an electric boiler system, with base board radiators. I also have an outdoor wood burner that heats the system, and bypasses the electric boiler, but uses the same pump. The valve opening and closing can be quite confusing. We bought this home last year, and luckily, the previous owner had all valves tagged with instructions. The installer should be there getting the new equipment working properly, or replacing it!!!
If your mind draws a blank, turn off the sound, because ya can't learn a thing if you're doin all the talkin
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051879
01/16/24 08:54 PM
01/16/24 08:54 PM
|
Joined: Jan 2020
Posts: 4,951 Aliceville, Kansas 43
Yukon John
trapper
|
trapper
Joined: Jan 2020
Posts: 4,951
Aliceville, Kansas 43
|
Looks to me like you need to raise some Cain with the install company. I personally would not be very pleasing to deal with if it were me.
Act like a blank, get treated like a blank. Insert your own blank!
|
|
|
Re: New furnace is junk.
[Re: sweetwilliam]
#8051883
01/16/24 08:56 PM
01/16/24 08:56 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Are those some kind of a compression joint on the pipes? Have seen a lot of problems with the welded joints in New pvc pipes with over compressing the joint and restricting water flow. Yes everything is compression fittings.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051908
01/16/24 09:15 PM
01/16/24 09:15 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Can you hear gurgling in the lines. That would indicate running in the wrong direction but wouldn't cause poor heat. Are there bleeder valves in the highest part of the system or is the bladder tank (gray one) where the auto bleeder is?
You probably are air locked!
Last edited by Oh Snap; 01/16/24 09:16 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051953
01/16/24 09:54 PM
01/16/24 09:54 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Is the fin tube fed from below? You said in an earlier post that the pipes on each side of the fin tube were hot but the fin tube was cool. If fed from below the water could be air blocked in the fin tube and trickling through and the pipes on each side be holding water thus be hot.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8051970
01/16/24 10:06 PM
01/16/24 10:06 PM
|
Joined: Oct 2009
Posts: 7,429 western mn
bucksnbears
trapper
|
trapper
Joined: Oct 2009
Posts: 7,429
western mn
|
Gotta ask..., what made you buy a fuel oil one?
swampgas chili and schmidt beer makes for a deadly combo
You have to remember that 1 out of 3 Democratic Voters is just as dumb as the other two.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052300
01/17/24 10:23 AM
01/17/24 10:23 AM
|
Joined: Mar 2014
Posts: 1,325 vermont
vermontster
trapper
|
trapper
Joined: Mar 2014
Posts: 1,325
vermont
|
Sounds like they should purge the air from the system, if the pipes have air in them the water won’t flow through the pipes and the system won’t automatically purge the air out. Is the house two stories? If so you may have to run the boiler water pressure up around 18-20 psi.
The bitterness of poor quality last a lot longer than the sweetness of low price
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052436
01/17/24 12:56 PM
01/17/24 12:56 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
901
To me the key to fixing the problem is where OP said heat on each side of fin tube and fin tube is cooler. Airlock IMO.
Wouldn't undersized boiler use more fuel and run a lot more? He said he is using a lot of fuel.
Last edited by Oh Snap; 01/17/24 12:58 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052471
01/17/24 01:37 PM
01/17/24 01:37 PM
|
Joined: Dec 2006
Posts: 9,709 ND
MJM
trapper
|
trapper
Joined: Dec 2006
Posts: 9,709
ND
|
Wouldn't an air lock cause it to use more fuel too. The water is hot but not going any where it thinks its cold. It sounds like it is burning plenty of fuel. I switched over to my second 500 gallon propane tank on the 6th of Jan. I have forced air.
"Not Really, Not Really" Mark J Monti "MJM you're a jerk."
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052483
01/17/24 01:42 PM
01/17/24 01:42 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
I have limited experience with propane systems except temporary propane unit heaters during really cold and it turning to liquid. It seems that the furnace is computer controlled and it may not be able to figure out that there is a problem so just burning fuel.
Not sure if it is still a problem since OP hasn't commented since last evening.
Last edited by Oh Snap; 01/17/24 01:43 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: Oh Snap]
#8052496
01/17/24 01:52 PM
01/17/24 01:52 PM
|
Joined: Nov 2017
Posts: 244 PA
Snyde901
trapper
|
trapper
Joined: Nov 2017
Posts: 244
PA
|
Wouldn't undersized boiler use more fuel and run a lot more? He said he is using a lot of fuel.
Yes, agreed and that's what the second service tech diagnosed as well and the problem seemed to surface during sub zero temps. Hard to say for sure without being there but if the entering & leaving pipes are both hot but the fins are cooler, the heat is being transferred to the air flowing across them which is normal. The return temp & boiler cycle times would be telling. If supply & return temps are decent but the boiler is running continuously and the house isn't getting warmer just screams undersized. I ruled out the air lock only because with as many techs were troubleshooting it, surely they'd find that...but you never know
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052552
01/17/24 02:40 PM
01/17/24 02:40 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
There is a big difference between residential and commercial heating tech's.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052617
01/17/24 03:33 PM
01/17/24 03:33 PM
|
Joined: Mar 2014
Posts: 1,325 vermont
vermontster
trapper
|
trapper
Joined: Mar 2014
Posts: 1,325
vermont
|
Usually the zone valves ( gray boxes with wires coming out above the circulator pump) have a spring loaded lever located under the wires. If the zone valves are open and allowing water to flow through you can move the lever with no resistance, if the lever moves but with resistance then the zone valves aren’t open. I assume they are working. You can also manually lock the zone valves open with the lever by pushing it open and then push it behind the notch in the housing
The bitterness of poor quality last a lot longer than the sweetness of low price
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052622
01/17/24 03:36 PM
01/17/24 03:36 PM
|
Joined: Mar 2014
Posts: 1,325 vermont
vermontster
trapper
|
trapper
Joined: Mar 2014
Posts: 1,325
vermont
|
The gray tank on the floor is the systems expansion tank, it allows the heated water to expand and not cause the pressure to rise. The brass unit on top of it a spiravent and it removes the air from the system as the water flows through it.
The bitterness of poor quality last a lot longer than the sweetness of low price
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8052905
01/17/24 08:18 PM
01/17/24 08:18 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
If one section of fin tube has an airlock and hot water is passing through but because of air its partial it would effect the whole system. Auto bleeders are notorious for not working.
Maybe the OP has fixed the problem! Would be good to know the outcome and that they are warm!
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053065
01/17/24 10:43 PM
01/17/24 10:43 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
If you look close at the stainless steel tubing coming out of the boiler the arrow on the manifold points to the right for flow. And the pump is pushing water to the left. They have the pump going the wrong direction.
They didn't change it, they want to till tomorrow.
Last edited by 1lessdog; 01/17/24 10:45 PM.
|
|
|
Re: New furnace is junk.
[Re: Posco]
#8053092
01/17/24 11:05 PM
01/17/24 11:05 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
Easy enough to reverse the circulator. They will push the water into the return lines. How will that work? I open just about all the bleeder valves on the registers. There was no air.
Last edited by 1lessdog; 01/17/24 11:07 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053093
01/17/24 11:06 PM
01/17/24 11:06 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Too bad you have to wait another day! Easy fix he should have done it.
I am not so sure that is the problem. Years ago I installed my boiler and the pump was running the wrong direction. It worked for many years that way until I had a new boiler installed and that's when I found out. It just was always noisy!
Last edited by Oh Snap; 01/17/24 11:09 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: Posco]
#8053103
01/17/24 11:14 PM
01/17/24 11:14 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
It looks like a pretty clean install. They should have you on your way in a matter of minutes. They isolated the circulator well. Can they push water away from the boiler and expansion and bleeder tank.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053115
01/17/24 11:37 PM
01/17/24 11:37 PM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
It looks like a pretty clean install. They should have you on your way in a matter of minutes. They isolated the circulator well. Can they push water away from the boiler and expansion and bleeder tank. Sure.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053125
01/17/24 11:58 PM
01/17/24 11:58 PM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
Easy enough to reverse the circulator. They will push the water into the return lines. How will that work? I open just about all the bleeder valves on the registers. There was no air. Don't sweat it. Those small vents are designed to remove residual air (small amounts) in the system. I would imagine your plumber will purge the system after he reverses the circulator. It's a very straightforward process you can do yourself once you've been shown how.
|
|
|
Re: New furnace is junk.
[Re: Posco]
#8053220
01/18/24 08:06 AM
01/18/24 08:06 AM
|
Joined: Nov 2017
Posts: 244 PA
Snyde901
trapper
|
trapper
Joined: Nov 2017
Posts: 244
PA
|
Will they turn the pump or just rewire it? Turn it 180 degrees. Not that simple, those zone valves are also directional as are some air scoops. They are going to have to reverse piping assuming the zv's are on return where they should be. Still curious as to what that unit is hanging to the left of the boiler.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053249
01/18/24 08:42 AM
01/18/24 08:42 AM
|
Joined: Nov 2017
Posts: 244 PA
Snyde901
trapper
|
trapper
Joined: Nov 2017
Posts: 244
PA
|
Correct they can go on supply or return but return is preferred for ZV's, those Honeywell ZV's absolutely impede flow if installed in the wrong direction. I looked up the piping diagram for that boiler, it shows return connection is on the right side so according to OP the pump is correct, maybe they installed the SS primary header backwards? Seems that unit to the left is a hydronic air handler
Last edited by Snyde901; 01/18/24 08:44 AM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053450
01/18/24 12:02 PM
01/18/24 12:02 PM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
That is the Electric 30KW boiler. They took unhooked it now it doesn't work. I asked the boss man yesterday when they were going to fix it. He asked why it was taken apart. I don't know. Any progress?
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053472
01/18/24 12:28 PM
01/18/24 12:28 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
What are your temperatures there today?
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053500
01/18/24 01:04 PM
01/18/24 01:04 PM
|
Joined: Mar 2018
Posts: 2,238 Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Posts: 2,238
Missouri
|
About 20 years ago, I took over what amounted to building superintendent duties on a 3 story residential structure. Original part was about 100 years old and was heated by live steam. About 50 years prior, an addition was put on and it was heated by hot water radiant heat.........using live steam thru a heat exchanger to heat the water. The commercial furnace guy met me one day to go over the entire system. How it was designed......how it worked. My first impression was it was only slightly more complicated than a nuclear submarine.......but over time, came to realize the brilliance of the system. A mechanical marvel designed and built 50 to 100 years ago by some truly genius minds. Heating guy referred to them as "the ancients".
Fast forward 10 years, in sections where the hot water radiant heat system pipes passed thru......the two upper floors.......got gutted and remodeled one summer. We get into late fall and the heat comes on........yet no heat on the two upper floors. Talked to commercial contractor what did the remodel work and they assured me it was working. Went back to the commercial heating expert and we talk thru it. Long story short, after I (just me) spent two days messing with it concluded that during the remodel, they had cut and capped the circulation pipes. No more loop......only two dead ends. It took me and the commercial heating guy almost two hours to convince the general contractor, his plumbing sub contractor and two architects they had screwed the pooch. Their understanding........and even ability to understand it......was abysmal. It took them nearly 2 weeks and tens of thousands of $ to come back to rip out the finish so they could fix it. Somebody's E & O took a big hit.
My takeaway was if these systems are designed and installed right, they both simple and highly effective way to heat some space. If not, they can be a nightmare to deal with.
My other takeaway was even 20 year ago, the commercial boiler guy was charging about $100 per hour.......probably closer to $150 per hour or more today. If I was a young guy who had a mind for mechanical systems, there is a wide open career path for you. Buildings with these systems in place swill exist and there is a need for experts who understand how to keep them running. A forced air HVAC system is one thing. Commercial rated live steam boilers are something else entirely. Along the lines of brain surgery isn't hard if you know how. Those that know how can make a lot of money.
Last edited by HayDay; 01/18/24 01:12 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053514
01/18/24 01:16 PM
01/18/24 01:16 PM
|
Joined: Mar 2018
Posts: 2,238 Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Posts: 2,238
Missouri
|
I have been on the phone with the office and tech. I think there trying to figure out what they need to do. What they need to do is show up to put eyes on what they did and what they got. They are not going to figure it out somewhere else.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053516
01/18/24 01:17 PM
01/18/24 01:17 PM
|
Joined: Dec 2006
Posts: 184 PA
PadCatch
trapper
|
trapper
Joined: Dec 2006
Posts: 184
PA
|
I’m currently an HVAC estimator but was an installer and service tech for many years. That boiler is obviously a condensing boiler (pvc flue piping) one thing I do know about condensing boilers is that they have an outdoor sensor (to change firing rate of boiler according to load condition of home). Was this installed? If so, was it installed where the flue exhaust is actually discharging right on the outdoor sensor? This will prevent the boiler from high firing thinking that it’s actually warmer outside than it really is. I know I saw that you had an oil boiler currently and I just find it odd that a brand new 95% condensing boiler is not handling this load. (You have very minimal heat lost through the pvc exhaust) the oil boiler probably had around 400* flue temp. Your actual boiler sizing drops whenever you installer this high efficiency equipment. That new boiler probably has around a 90* flue temp. I know I don’t like the positioning of that circulator. It appears to be on an angle which will cause that circulator to trip on thermal overload. (Its definitely going to burn that circulator up). I do believe that’s your secondary loop pump. There’s suppose to be a primary pump inside that boiler. Did the 30KW no longer being used heat the home alright? 30,000 watts X 3.4 btu = 102,000btu/hr
Disregard what I said about the circulator. I just looked at the pics and realized the photo was flopped. It is in a correct position concerning the shaft.
Last edited by PadCatch; 01/18/24 01:37 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8053847
01/18/24 08:10 PM
01/18/24 08:10 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
The installer never showed up today. There waiting to here back from Navian. I told the worker it's been a week since we had good heat. I talked Navian tech support and he said water should flow to the left. I told him arrow says right. He than told me sticker is on backwards. I said it it's backwards the lettering would be backwards and it's not. This weekend is a high of 6 below zero with lows of 15 below. If we don't have a bunch of electric heater on the house will freeze up.
Yes electric boiler worked good till they took it apart.
Last edited by 1lessdog; 01/18/24 08:12 PM.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8054040
01/18/24 10:54 PM
01/18/24 10:54 PM
|
Joined: Oct 2009
Posts: 7,429 western mn
bucksnbears
trapper
|
trapper
Joined: Oct 2009
Posts: 7,429
western mn
|
Seems like a total disaster to me!
What happens to an easy propane furnace hooked up to simple duct work?
swampgas chili and schmidt beer makes for a deadly combo
You have to remember that 1 out of 3 Democratic Voters is just as dumb as the other two.
|
|
|
Re: New furnace is junk.
[Re: Snyde901]
#8054456
01/19/24 01:20 PM
01/19/24 01:20 PM
|
Joined: Feb 2007
Posts: 673 N. Dakota
1lessdog
OP
trapper
|
OP
trapper
Joined: Feb 2007
Posts: 673
N. Dakota
|
So the electric boiler was in addition to the fuel oil boiler you had? Did the new boiler work when it was warmer outside?
The new boiler could be faulty, I've installed a lot of boilers without issue but the one for my own garage doesn't work as it should. It's plenty big enough but it will never modulate down, always runs at 100% and can't get the water temp over 120, which works for in floor. It keeps the space at temp but runs more than it should, but gas is free so it doesn't matter. I can get it to modulate by slowing pumps down but that throws my delta T way out of whack. I've had the rep there running diagnostics, replaced gas valve, talked to factory, no resolution, it just doesn't do what it should. They hooked my up with there newer model but it's still sitting in the crate. I'm glad it was mine & not a customers but average person wouldn't know since space temp is satisfied. Yes,electric boiler worked. We get a better rate from power company with dual fuel. Yes the new boiler worked when warmer outside.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8054509
01/19/24 02:23 PM
01/19/24 02:23 PM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
The installers are back working on it. The exhaust pipe is to small according to the manufacturer. They are also moving the pump from the return side to the supply side. Will see if any of it helps. That's going to be invasive. Let us know how you make out.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8054550
01/19/24 03:23 PM
01/19/24 03:23 PM
|
Joined: Mar 2014
Posts: 1,325 vermont
vermontster
trapper
|
trapper
Joined: Mar 2014
Posts: 1,325
vermont
|
The zone valves are also directional. They have an arrow on the brass body pointing to the direction of the flow of water.
The bitterness of poor quality last a lot longer than the sweetness of low price
|
|
|
Re: New furnace is junk.
[Re: HayDay]
#8055232
01/20/24 12:58 PM
01/20/24 12:58 PM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
So they got it running on all cylinders?
What was wrong? I'm interested as well.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8055234
01/20/24 01:00 PM
01/20/24 01:00 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
I have 5 zones with one pump and its oil fired. Never have had a problem so seems to me the company that installed your system has some fixing to do. Good Luck and Thanks for keeping us in the other LOOP!
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8055908
01/20/24 11:56 PM
01/20/24 11:56 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Is your house well insulated?
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: Oh Snap]
#8055920
01/21/24 12:05 AM
01/21/24 12:05 AM
|
Joined: Nov 2017
Posts: 11,314 Maine, Aroostook
Posco
trapper
|
trapper
Joined: Nov 2017
Posts: 11,314
Maine, Aroostook
|
Is your house well insulated? Or inadequate baseboard but he said the oil-fired unit kept up fine.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8056037
01/21/24 07:06 AM
01/21/24 07:06 AM
|
Joined: Nov 2017
Posts: 244 PA
Snyde901
trapper
|
trapper
Joined: Nov 2017
Posts: 244
PA
|
With a high of 8 degrees today and 30 mph S wind and all thermostat set at 72 and the highest the house got was 67 degrees.
They know there's a problem, they just don't know what to do. Install a bigger boiler or fire up your electric boiler up to supplement the combi on the colder days. We put bigger boilers in smaller houses here in PA, with the turndown ratios on the condensing boilers oversizing is a non issue.
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8058025
01/23/24 12:06 PM
01/23/24 12:06 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
The house was built in 1974. We put new windows in 10 yrs ago and they put in blow in insulation. The Fuel oil boiler had no problem keeping up on the coldest days. It could be 20 below zero, with a 30 mph wind and it still kept the house at 70 degrees. They know there's a problem, they just dont know what to do to fix it. I hope they figure it out before the cold goes away and tested so you will know for next winter!. Thanks for the update!
Last edited by Oh Snap; 01/23/24 01:11 PM.
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8058174
01/23/24 03:10 PM
01/23/24 03:10 PM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Don't leet them let the test cold to go away then next winter deal with it again!
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
Re: New furnace is junk.
[Re: 1lessdog]
#8060357
01/26/24 01:41 AM
01/26/24 01:41 AM
|
Joined: Feb 2021
Posts: 2,365 Interior Alaska
Oh Snap
trapper
|
trapper
Joined: Feb 2021
Posts: 2,365
Interior Alaska
|
Have they ever fixed the problem?
I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
|
|
|
|
|