Can I take a 220 a/c outlet and convert to two 110 outlets? Breakers would have to be separated. Thanks in advance
the just shall live by faith
member FTA, ATA, EAFT 1776 - the year we told a tyrant we weren't to be under a dictator Caveat ater macula
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277548
12/03/24 03:23 PM
12/03/24 03:23 PM
|
Joined: Jun 2018
Beatrice, NE
loosegoose
trapper
|
trapper
Joined: Jun 2018
Beatrice, NE
|
Yes. That exact thing is done in kitchens sometimes, where 2 20A 110V circuits are required for the outlets. The black hot and red hot wires are wired to every other outlet, and the white neutral and green ground are wired to every outlet.
Last edited by loosegoose; 12/03/24 03:23 PM.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277565
12/03/24 03:41 PM
12/03/24 03:41 PM
|
Joined: Sep 2007
central wisconsin
deerfly
trapper
|
trapper
Joined: Sep 2007
central wisconsin
|
Certainly would work but I believe you would want the breaker bonded if using single pole breakers, one trip, both trip. Or a 2 pole breaker. You wouldn't one to fault and have the other phase putting load on the shared neutral if in use. I am not an elecrician
Last edited by deerfly; 12/03/24 03:42 PM.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277569
12/03/24 03:49 PM
12/03/24 03:49 PM
|
Joined: Dec 2023
Minnesota
30-06 Trapper
trapper
|
trapper
Joined: Dec 2023
Minnesota
|
Ignore the part where it says dont mess with this on your own I think he might have thought I was going to be doing it
The rifle has no will of its own it may be used for evil but there are more good men than evil men and evil will be corrected by good men with rifles.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277577
12/03/24 04:02 PM
12/03/24 04:02 PM
|
Joined: Dec 2010
central arkansas
the Blak Spot
OP
trapper
|
OP
trapper
Joined: Dec 2010
central arkansas
|
Thanks for all the replies!
the just shall live by faith
member FTA, ATA, EAFT 1776 - the year we told a tyrant we weren't to be under a dictator Caveat ater macula
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: Cragar]
#8277672
12/03/24 07:00 PM
12/03/24 07:00 PM
|
Joined: Feb 2024
Iowa
slue-foot
trapper
|
trapper
Joined: Feb 2024
Iowa
|
Not code acceptable. You cannot share a neutral between 2 phases. The neutral is considered a load carry conductor. Reason to this is if 1 circuit breaker is tripped the neutral would still carry the current of the 2 circuit.
Last edited by slue-foot; 12/03/24 07:03 PM. Reason: added final sentence
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277702
12/03/24 07:52 PM
12/03/24 07:52 PM
|
Joined: Mar 2018
Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Missouri
|
Not sure about the code compliance, but seems to me you could use existing wiring........swap out the 220 breaker to a 110 breaker using black hot, neutral and ground, then run two outlets in series as with any standard circuit. The second 220 hot line.......red wire if there is one......goes dead.
Easy to vote your way into socialism, but impossible to vote your way out of it.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: HayDay]
#8277716
12/03/24 08:14 PM
12/03/24 08:14 PM
|
Joined: Dec 2010
central arkansas
the Blak Spot
OP
trapper
|
OP
trapper
Joined: Dec 2010
central arkansas
|
Not sure about the code compliance, but seems to me you could use existing wiring........swap out the 220 breaker to a 110 breaker using black hot, neutral and ground, then run two outlets in series as with any standard circuit. The second 220 hot line.......red wire if there is one......goes dead. Like this?
the just shall live by faith
member FTA, ATA, EAFT 1776 - the year we told a tyrant we weren't to be under a dictator Caveat ater macula
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277738
12/03/24 08:44 PM
12/03/24 08:44 PM
|
Joined: Mar 2018
Missouri
HayDay
trapper
|
trapper
Joined: Mar 2018
Missouri
|
Yes, except to avoid confusion, would pull the 220 breaker, and assuming #10 wire, would install a single 20 amp 110 breaker and a blank filler. Then use 20 amp outlets. Might tape the red and black wires together in the service panel to indicate they had once been used together, but then put wire nut on both ends of the red wire. Rigged that way, they could be put back to 220 use at some point in the future.
Easy to vote your way into socialism, but impossible to vote your way out of it.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277745
12/03/24 08:51 PM
12/03/24 08:51 PM
|
Joined: Feb 2024
Iowa
slue-foot
trapper
|
trapper
Joined: Feb 2024
Iowa
|
Totally acceptable. Take the red wire in the panel and double it back on itself and tape close along with wire nutting the dead end in the first outlet/junction box. I go 1 step further and label the wire as dead leg on the white outer cover if you can. I always give the next electrician who follows my work a heads-up on what they are looking at.
Last edited by slue-foot; 12/03/24 08:53 PM. Reason: changed sentence
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: the Blak Spot]
#8277776
12/03/24 09:27 PM
12/03/24 09:27 PM
|
Joined: Oct 2024
Kansas
someGuyInKansas
trapper
|
trapper
Joined: Oct 2024
Kansas
|
failure modes get funky and dangerous. For example, if the neutral wire breaks, and you have a load on both outlets, but an uneven load, each outlet will 'see' something different from the 120 they should see. For simplicity, assume there's a motor on each outlet and one of them draws twice the current as the other, and the nuetral breaks. Without the neutral carrying load to the breaker box, you've got 240 across the pair of motors in series, but one has twice the resistance of the other. So one sees 80v and the other sees 160. If either shuts off the other shuts off too. This is unlikely, but possible.
Another thing to keep in mind: it is critical that the two hot wires come off different legs in the breaker box. With them coming off different legs, the neutral only carries the imbalance (the critical point is: the neutral never carries more than the hot wire). If a few years from now someone rearranges the wires in the box and now the two hots are on the same leg, the neutral is carrying the sum of both hot wires instead of the difference. i.e. it can carry up to double what its rated for. That can very easily burn your house down.
When my dad was considering running a wire across a field, I suggested he buy 12/3 instead of 12/2, specifically for this reason. For slighly more money, he could have twice the power available. But you do need to be careful with it.
|
|
|
Re: OT: 220 outlet -> 110 ?
[Re: someGuyInKansas]
#8277806
12/03/24 10:10 PM
12/03/24 10:10 PM
|
Joined: Feb 2014
Ky
jbyrd63
trapper
|
trapper
Joined: Feb 2014
Ky
|
failure modes get funky and dangerous. For example, if the neutral wire breaks, and you have a load on both outlets, but an uneven load, each outlet will 'see' something different from the 120 they should see. For simplicity, assume there's a motor on each outlet and one of them draws twice the current as the other, and the nuetral breaks. Without the neutral carrying load to the breaker box, you've got 240 across the pair of motors in series, but one has twice the resistance of the other. So one sees 80v and the other sees 160. If either shuts off the other shuts off too. This is unlikely, but possible.
Another thing to keep in mind: it is critical that the two hot wires come off different legs in the breaker box. With them coming off different legs, the neutral only carries the imbalance (the critical point is: the neutral never carries more than the hot wire). If a few years from now someone rearranges the wires in the box and now the two hots are on the same leg, the neutral is carrying the sum of both hot wires instead of the difference. i.e. it can carry up to double what its rated for. That can very easily burn your house down.
When my dad was considering running a wire across a field, I suggested he buy 12/3 instead of 12/2, specifically for this reason. For slighly more money, he could have twice the power available. But you do need to be careful with it. If youre feeding a 220 circuit legs off one single pole breaker you need to be a plumber!!!
|
|
|
|
|