10/24/21 01:30 PM
10/24/21 01:30 PM
Joined: Nov 2010
Posts: 1,533
USA-WI
K
Kre Offline OP
trapper
Kre  Offline OP
trapper
K

Joined: Nov 2010
Posts: 1,533
USA-WI
I started the furnace for the first time this morning. It took me a while to notice i wasn't getting heat.

I reset the flame rollout switch and it appears to be fine.

Burner looks good through the site glass.

Should I be concerned? Should I have someone come out and look at it?

Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387002
10/24/21 01:40 PM
10/24/21 01:40 PM
Joined: Dec 2006
Posts: 2,302
Waterville Minnesota
M
mudtracker Offline
trapper
mudtracker  Offline
trapper
M

Joined: Dec 2006
Posts: 2,302
Waterville Minnesota
I guess I would wait and see if you have any more issues.


WHO MADE THIS MESS ALL OVER MY FLOOR THE MUDTRACKER WAS HERE HE HE HE
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387006
10/24/21 01:43 PM
10/24/21 01:43 PM
Joined: Nov 2010
Posts: 1,533
USA-WI
K
Kre Offline OP
trapper
Kre  Offline OP
trapper
K

Joined: Nov 2010
Posts: 1,533
USA-WI
I had a new hot water heater installed about 2 weeks ago and they had to turn off gas to the house. I wonder if this had something to do with it?

I'm keeping a close eye on it. It's heating well and the flame looks good.

Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387014
10/24/21 01:54 PM
10/24/21 01:54 PM
Joined: Feb 2017
Posts: 225
PA
Charles2 Offline
trapper
Charles2  Offline
trapper

Joined: Feb 2017
Posts: 225
PA
A roll out switch is a temp sensor near the burners. It s job is to trip and prevent flame roll out in front of burners due to possible flue blockage or other causes. Gas disruption should not cause it to trip. To be sure there is not a safety issue your furnace and venting should be checked.


Charles2Trap
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387019
10/24/21 02:01 PM
10/24/21 02:01 PM
Joined: Nov 2010
Posts: 1,533
USA-WI
K
Kre Offline OP
trapper
Kre  Offline OP
trapper
K

Joined: Nov 2010
Posts: 1,533
USA-WI
I read that low gas pressure could cause this. That's what made me think about the gas being turned off recently.

I'm keeping a close eye on it.

Charles, When would you feel comfortable it was just a fluke?

Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387031
10/24/21 02:15 PM
10/24/21 02:15 PM
Joined: Feb 2017
Posts: 225
PA
Charles2 Offline
trapper
Charles2  Offline
trapper

Joined: Feb 2017
Posts: 225
PA
Propane furnaces can be affected by low pressure, but, usually there is a low pressure switch in the gas line before the gas valve to prevent it. Also, depends if furnace is vented by a inducer (motor) or is atmospheric (chimney) draft. Inducer problem or chimney blockage are examples of restricted or poor venting that can cause roll out switch to trip. Any gas should be a steady pressure, so a steady flow through the gas valve and burners, whether gas or venting air. So, no back flow from burners if venting is proper. If, there is an issue , the roll out will trip again. How long that will take is unknown.


Charles2Trap
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387032
10/24/21 02:17 PM
10/24/21 02:17 PM
Joined: Feb 2017
Posts: 225
PA
Charles2 Offline
trapper
Charles2  Offline
trapper

Joined: Feb 2017
Posts: 225
PA
Also, a blockage in the heat exchanger can cause roll out to trip.


Charles2Trap
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387035
10/24/21 02:20 PM
10/24/21 02:20 PM
Joined: Nov 2010
Posts: 1,533
USA-WI
K
Kre Offline OP
trapper
Kre  Offline OP
trapper
K

Joined: Nov 2010
Posts: 1,533
USA-WI
It sounds like I should have someone come to take a look at it.

Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387045
10/24/21 02:27 PM
10/24/21 02:27 PM
Joined: Feb 2017
Posts: 225
PA
Charles2 Offline
trapper
Charles2  Offline
trapper

Joined: Feb 2017
Posts: 225
PA
For safety sake, I recommend it.


Charles2Trap
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387050
10/24/21 02:30 PM
10/24/21 02:30 PM
Joined: Sep 2013
Posts: 21,411
Green County Wisconsin
G
GREENCOUNTYPETE Offline
trapper
GREENCOUNTYPETE  Offline
trapper
G

Joined: Sep 2013
Posts: 21,411
Green County Wisconsin
if you have air in the lines it can take a few tries to get enough through it at start up to purge the line

when I installed my hot water heater it is the forced exhaust type , about 4-5 times turn it on let it try to start before it finally did that first time been fine since


America only has one issue, we have a Responsibility crisis and everything else stems from it.
Re: HVAC Guys: flame rollout switch? [Re: GREENCOUNTYPETE] #7387059
10/24/21 02:35 PM
10/24/21 02:35 PM
Joined: Feb 2017
Posts: 225
PA
Charles2 Offline
trapper
Charles2  Offline
trapper

Joined: Feb 2017
Posts: 225
PA
Failed ignition due to air in the gas lines does not cause the roll out to trip, it only causes unit to cycle until air is purged. Your forced exhaust makes that happen.


Charles2Trap
Re: HVAC Guys: flame rollout switch? [Re: Kre] #7387422
10/24/21 09:39 PM
10/24/21 09:39 PM
Joined: Dec 2006
Posts: 10,492
ND
M
MJM Offline
trapper
MJM  Offline
trapper
M

Joined: Dec 2006
Posts: 10,492
ND
I saw where the OP said he reset the roll out switch, but I never saw him say it was tripped.


"Not Really, Not Really"
Mark J Monti
"MJM you're a jerk."
Re: HVAC Guys: flame rollout switch? [Re: MJM] #7387605
10/25/21 08:24 AM
10/25/21 08:24 AM
Joined: Nov 2010
Posts: 1,533
USA-WI
K
Kre Offline OP
trapper
Kre  Offline OP
trapper
K

Joined: Nov 2010
Posts: 1,533
USA-WI
Originally Posted by MJM
I saw where the OP said he reset the roll out switch, but I never saw him say it was tripped.


You know...I can't say for sure that it was tripped. When I pressed the button, it didn't seem to do much. But, the LED blinks said it was the flame rollout switch. I pressed the button. Then the thing started and ran fine ever since.

The house it a lot warmer than I'd like it to be.

Previous Thread
Index
Next Thread