Construction Guys #8517267
11 hours ago
11 hours ago
Joined: Sep 2013
Nevada
N
nvwrangler Offline OP
trapper
nvwrangler  Offline OP
trapper
N

Joined: Sep 2013
Nevada
I picked up a new safe on a black Friday sale and need to reenforce the floor before putting it in place, The question is whats the best way to do that?

safe foot print 28 x 50, 880 lbs

joists are 16 in centers and is being placed against a load bearing wall, center of house with pillars and beam support under the house

Planning on cement pier blocks with trailer type leveling jacks holding a 4x6 , don't know if I can get a 6 foot 4x6 under the house to be able to support 4 joists or if a 4 foot 4x6 and only catching 3 joists will be enough? Planning on 2 spots of support front and back of safe

Re: Construction Guys [Re: nvwrangler] #8517279
10 hours ago
10 hours ago
Joined: Dec 2011
MT
S
snowy Online content
trapper
snowy  Online Content
trapper
S

Joined: Dec 2011
MT
You must have a stash for that big safe. I have no opinion or options for your restructuring. I have one small 2 x 2 foot that suffice my needs.


Give me a fish, I will eat for a day. Teach me to fish, I will eat for a lifetime
Re: Construction Guys [Re: nvwrangler] #8517283
10 hours ago
10 hours ago
Joined: Jun 2010
Iowa
~ADC~ Offline
The Count
~ADC~  Offline
The Count

Joined: Jun 2010
Iowa
How much space between the bottom of the joists and the ground?

Re: Construction Guys [Re: ~ADC~] #8517290
10 hours ago
10 hours ago
Joined: Sep 2013
Nevada
N
nvwrangler Offline OP
trapper
nvwrangler  Offline OP
trapper
N

Joined: Sep 2013
Nevada
Originally Posted by ~ADC~
How much space between the bottom of the joists and the ground?



Maybe 2.5 feet or 3 to the bottom of the joists

Re: Construction Guys [Re: snowy] #8517291
10 hours ago
10 hours ago
Joined: Sep 2013
Nevada
N
nvwrangler Offline OP
trapper
nvwrangler  Offline OP
trapper
N

Joined: Sep 2013
Nevada
Originally Posted by snowy
You must have a stash for that big safe. I have no opinion or options for your restructuring. I have one small 2 x 2 foot that suffice my needs.


My son in laws that have to help move it think I should get 2 smaller ones lol Need one this big so the guns have room to reproduce and multiply without the wife knowing lol

Last edited by nvwrangler; 10 hours ago.
Re: Construction Guys [Re: nvwrangler] #8517293
10 hours ago
10 hours ago
Joined: Mar 2019
Southern NJ
maintenanceguy Offline
trapper
maintenanceguy  Offline
trapper

Joined: Mar 2019
Southern NJ
Design live load (things that you can move) is 40lbs prer sq ft. Your safe is 110 lbs per sq ft. A lot more than design load but not enough to fall through. Design load is complicated. It's for an average load of 40 lbs per sq ft. If you set your safe in a place where there aren't other very heavy things around it, the beams contributing to supporting the safe can still be fine if the total load on that beam is still no more than 40 lbs per sq ft. It's even a little more complicated than than because weight at the center of a span is different than weight near the end of a span but I'm confident that you're okay. When the code is written, they know somebody is going to set a gun safe somewhere. If I was worried, I would measure the height of the bottom of the bean unloaded and then set the safe and measure how much deflection there is. Code wants only 1/240 of the span in deflection. So if your beam is 240 inches long, it's allowed to deflect 1 inch. If the deflection exceeded L/240 (it won't) I might care. I probably still don't because, unless my pool table is crooked, deflection doesn't matter much to me. I care about catastrophic failure and at 880 lb point load you're fine. We have people that heavy who walk around their houses (or roll around) every day and they don't fall through.

Re: Construction Guys [Re: maintenanceguy] #8517304
10 hours ago
10 hours ago
Joined: Sep 2013
Nevada
N
nvwrangler Offline OP
trapper
nvwrangler  Offline OP
trapper
N

Joined: Sep 2013
Nevada
Originally Posted by maintenanceguy
Design live load (things that you can move) is 40lbs prer sq ft. Your safe is 110 lbs per sq ft. A lot more than design load but not enough to fall through. Design load is complicated. It's for an average load of 40 lbs per sq ft. If you set your safe in a place where there aren't other very heavy things around it, the beams contributing to supporting the safe can still be fine if the total load on that beam is still no more than 40 lbs per sq ft. It's even a little more complicated than than because weight at the center of a span is different than weight near the end of a span but I'm confident that you're okay. When the code is written, they know somebody is going to set a gun safe somewhere. If I was worried, I would measure the height of the bottom of the bean unloaded and then set the safe and measure how much deflection there is. Code wants only 1/240 of the span in deflection. So if your beam is 240 inches long, it's allowed to deflect 1 inch. If the deflection exceeded L/240 (it won't) I might care. I probably still don't because, unless my pool table is crooked, deflection doesn't matter much to me. I care about catastrophic failure and at 880 lb point load you're fine. We have people that heavy who walk around their houses (or roll around) every day and they don't fall through.


I believe the joists are only 14 or 16 foot long from the outside wall to the center beam, and its a spare room with just a dresser and bed in it. If I make sure it spans 3 joists and its at the end of the joists that should also help with the load correct?

Re: Construction Guys [Re: nvwrangler] #8517342
9 hours ago
9 hours ago
Joined: Dec 2007
40 years Alaska, now back to O...
A
alaska viking Offline
"Made it two years not being censored"
alaska viking  Offline
"Made it two years not being censored"
A

Joined: Dec 2007
40 years Alaska, now back to O...
Retired General Contractor for 40 years here.
First thing: What size are your joists? A 2"x10" holds a lot more than a 2"x8".
Also, 3/4" sheeting is stronger than 5/8" between the joists and spreading the load. Just because you are over 3 joists doesn't mean the next joist over on either side of the loaded joists aren't doing a bit of the "carrying".
Think of a Baby Grand piano. The load is resting on 4 legs, and likely not directly centered on a joist. Rather, the sheeting is spreading the load to 2 joists.
I have fortified many floor systems using 4"x6" material and posts when adding tile to a large floor, for instance. While I wasn't concerned that the floor system could handle the additional weight, (a single box of floor tile is heavy!), I was concerned about floor deflection, resulting in cracked grout joints. I would typically use pier blocks with 4"x4" posts under the 4"x6"s every 4' or so.
For your situation, I would be comfortable with a 49-1/2" 4"x6", (that carries all 4 joists "out to out" in construction lingo), or even 4"x4" "beam", and 2 4"x4" posts resting on pier blocks.
800 pounds, plus whatever you put in it, isn't that great a load when spread out over a floor system that has ground support nearby.


Just doing what I want now.

Re: Construction Guys [Re: nvwrangler] #8517345
9 hours ago
9 hours ago
Joined: Jan 2012
Ohio
OhioBoy Offline
trapper
OhioBoy  Offline
trapper

Joined: Jan 2012
Ohio
I'd add something solid on the ground like those post blocks and then cut some some boards to length a fuzz long and pound them in putting the safe on stilts. Maybe use 2x6 or something. Maybe add a runners (headers) across the bottom of the joices. Depends on how much room ya got I guess.

Re: Construction Guys [Re: nvwrangler] #8517371
7 hours ago
7 hours ago
Joined: Oct 2023
OR
W
wws Offline
trapper
wws  Offline
trapper
W

Joined: Oct 2023
OR
really depends on what type of joist you have. I have built a couple homes but am not an expert. are they the manufactured joist? or 2x10, 2x8? I would trust the solid wood more than the glued up ones they use now. if solid wood add a board next to them, under house work is no fun.

wws

Re: Construction Guys [Re: nvwrangler] #8517376
7 hours ago
7 hours ago
Joined: Dec 2009
The Hill Country of Texas
Leftlane Offline
"HOSS"
Leftlane  Offline
"HOSS"

Joined: Dec 2009
The Hill Country of Texas
There are some smart guys helping put here Jeb so I will only add that if you do have solid floor joists boxing in an area similar to the foot print of the safe would be easy and then a few extra braces under it should double or triple the capacity real quick.


What"s good for me may not be good for the weak minded.
Captain Gus McCrae- Texas Rangers


Re: Construction Guys [Re: nvwrangler] #8517384
7 hours ago
7 hours ago
Joined: Oct 2013
LA
D
dixieland Offline
trapper
dixieland  Offline
trapper
D

Joined: Oct 2013
LA
Originally Posted by nvwrangler


Planning on cement pier blocks…………



You’re getting good advice above. I’ll add that you need to change “cement” to concrete. Especially if you’re talking to a contractor for a bid. They won’t take advantage of you so bad.

Re: Construction Guys [Re: nvwrangler] #8517386
6 hours ago
6 hours ago
Joined: Jun 2010
Iowa
~ADC~ Offline
The Count
~ADC~  Offline
The Count

Joined: Jun 2010
Iowa
I'd double check on the joist hangers, make sure they aren't just toe nailed in. If they have good galvanized hangers, I'll bet you'll be just fine. Most people wouldn't even think to look and just go set it in place, like me. smile

Re: Construction Guys [Re: nvwrangler] #8517437
4 hours ago
4 hours ago
Joined: Mar 2016
lewis county,new york
N
newfox1 Offline
trapper
newfox1  Offline
trapper
N

Joined: Mar 2016
lewis county,new york
Originally Posted by nvwrangler
I picked up a new safe on a black Friday sale and need to reenforce the floor before putting it in place, The question is whats the best way to do that?

safe foot print 28 x 50, 880 lbs

joists are 16 in centers and is being placed against a load bearing wall, center of house with pillars and beam support under the house

Planning on cement pier blocks with trailer type leveling jacks holding a 4x6 , don't know if I can get a 6 foot 4x6 under the house to be able to support 4 joists or if a 4 foot 4x6 and only catching 3 joists will be enough? Planning on 2 spots of support front and back of safe

This should work just fine, more than most would do.