Re: Metal roof question
[Re: patrapper1989]
#8172823
07/14/24 08:07 AM
07/14/24 08:07 AM
|
Joined: Dec 2006
Posts: 22,132 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 22,132
SEPA
|
In the past six years I've built two buildings with metal roofs. The first was my new wood shop. I stick-framed the rafters and sheathed them with 1/2 CDX plywood. I put 30lb felt over that and then the metal panels. The only issue I has was that when I decided to put snow guards on I had to use specialized glue because they want a minimum of 1.5" fasteners and I only had 1/2". I didn't want to add blocking between the rafters because I had already insulated and finished the ceiling. The glue has held through six winters so far.
The second building is a summer kitchen. I went with traditional 2 x 4 perlins over the rafters. Since the building will be heated I was worried about condensation issues, you can have condensation issues with steel roofs even without heat in the building. I bought 2" Dow polystyrene panels, ripped them to width on my table saw and fit them tightly into the rafter cavities under the perlins. I caulked the edges where needed. There will be faced fiberglass insulation in the cavities under the polystyrene.
I figure the polystyrene and fiberglass will create a thermal break and the polystyrene will drain any moisture into the soffit area.
I'm a general contractor but I'm not an expert on steel roofing, I don't do that much of it.
Eh...wot?
|
|
|
Re: Metal roof question
[Re: Lugnut]
#8172836
07/14/24 08:22 AM
07/14/24 08:22 AM
|
Joined: Jan 2016
Posts: 199 Pennsylvania
patrapper1989
OP
trapper
|
OP
trapper
Joined: Jan 2016
Posts: 199
Pennsylvania
|
In the past six years I've built two buildings with metal roofs. The first was my new wood shop. I stick-framed the rafters and sheathed them with 1/2 CDX plywood. I put 30lb felt over that and then the metal panels. The only issue I has was that when I decided to put snow guards on I had to use specialized glue because they want a minimum of 1.5" fasteners and I only had 1/2". I didn't want to add blocking between the rafters because I had already insulated and finished the ceiling. The glue has held through six winters so far.
The second building is a summer kitchen. I went with traditional 2 x 4 perlins over the rafters. Since the building will be heated I was worried about condensation issues, you can have condensation issues with steel roofs even without heat in the building. I bought 2" Dow polystyrene panels, ripped them to width on my table saw and fit them tightly into the rafter cavities under the perlins. I caulked the edges where needed. There will be faced fiberglass insulation in the cavities under the polystyrene.
I figure the polystyrene and fiberglass will create a thermal break and the polystyrene will drain any moisture into the soffit area.
I'm a general contractor but I'm not an expert on steel roofing, I don't do that much of it. Did it seem like the 1/2" plywood had enough holding power? That's a good point about the snow guards I didn't think about. I'm a carpenter by trade but like you I really don't get into metal roofing
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8172863
07/14/24 09:23 AM
07/14/24 09:23 AM
|
Joined: Dec 2006
Posts: 22,132 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 22,132
SEPA
|
I've had no issues with holding power on the shorter screws. They are approved by the manufacturer as long as you adhere to the specified screw pattern.
If you go that route and want snow guards, add a row or two to the rafter cavities in the proper locations. it would probably be easier to do that from outside before you sheath. But doing it from inside before you insulate would work too.
I wasn't going to use snow guards until the first good snow dumped an avalanche of snow from the roof onto my freshly plowed driveway. That's why I didn't frame for them.
I was skeptical of the glue-on snow guards at first. I used SnoBlox/SnoJax brand and their recommended Surebond SB190 Everseal and followed the installation instructions. I was pretty sure I was going to be picking up snow guards the following spring but so far, so good.
They are rated at a high shear strength but it's still significantly less than mechanically fastened guards.
Eh...wot?
|
|
|
Re: Metal roof question
[Re: newfox1]
#8172864
07/14/24 09:23 AM
07/14/24 09:23 AM
|
Joined: May 2017
Posts: 325 ontario
k9-hunter
trapper
|
trapper
Joined: May 2017
Posts: 325
ontario
|
Patrapper, 5/8” plywood for the roof deck, not osb. Ice and water on bottom and in valleys if you have any. And roof paper the rest. It’s like tyvek for the roof. I like the kind with the spider on it, scorpion maybe. That’s how we do it. did roofing for 35 years and just recently changed professions as a bad knee doesnt like being on a roof anymore so roof decking should be min1/2" ply do not use osb it will workbut you are looking at issues if any sort of moisture happens use ice and water in the valleys and roof edges as for roof underlayment synethic felt is not reccomended under steel roofs unless it is designed for steel which most are not i would use tyvek or old school tar paper to cover the roof decking you could strap your roof also but i would reccomomend strapping every foot instead of every two(you can still screw every 2') now for all you new roofers out there synethic felt is just garabage it is like putting a tarp on your roof condensation can not escape from it and will saturate the roof deck and eventually rot the roof yes i know the roofing companys reccommend it and they say it breathes well i have made almost all of the companies synethic felt at a factory i worked at in the winter if you dont believe me place a tarp over a car and let it sit the car will rust and be wet whenever the tarp is removed if it keeps water out it cant let water evaporate in the late 70s they tried something similar and all the roof decks rotted the reason shingle companies recomend roof underlayment is because they all have had class action laws suits agaisnt them in the past 25 yrs because of poor shingles water should never get too the under layment to start as forpeople saying tar paper sucks to this day you can strip a roof and its still good it gets wet and dries its just not safe to walk on
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8172866
07/14/24 09:26 AM
07/14/24 09:26 AM
|
Joined: Dec 2006
Posts: 22,132 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 22,132
SEPA
|
I agree with you about the synthetic felt.
Eh...wot?
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8172964
07/14/24 12:31 PM
07/14/24 12:31 PM
|
Joined: Dec 2009
Posts: 22,565 The Hill Country of Texas
Leftlane
"HOSS"
|
"HOSS"
Joined: Dec 2009
Posts: 22,565
The Hill Country of Texas
|
The snap lock metal roofing design eliminates the fasteners threading their way out after 15 or 20 years ( less if you use shorter fasteners, OSB vs. CDX, or thinner decking to save a few bucks). In any of those cases, saving some money may see your 50 or 100 year roofing system fail in less than 20. I dont consider that a good trade.
The snap lock roofing does not address condensation, especially a relatively warm moist environment below a cold dry one. In that scenario the fasteners don't back out but instead collect excess moisture and rust in two prematurely.
�What�s good for me may not be good for the weak minded.� Captain Gus McCrae- Texas Rangers
|
|
|
Re: Metal roof question
[Re: Leftlane]
#8172969
07/14/24 12:39 PM
07/14/24 12:39 PM
|
Joined: Mar 2023
Posts: 3,168 WI
WI Outdoors
trapper
|
trapper
Joined: Mar 2023
Posts: 3,168
WI
|
The answer to that riddle is ventilation. And insulation.
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8172974
07/14/24 12:44 PM
07/14/24 12:44 PM
|
Joined: Dec 2009
Posts: 22,565 The Hill Country of Texas
Leftlane
"HOSS"
|
"HOSS"
Joined: Dec 2009
Posts: 22,565
The Hill Country of Texas
|
As far as insulation, it would have to be applied inside of the end of the fastener, in between them does no good.
�What�s good for me may not be good for the weak minded.� Captain Gus McCrae- Texas Rangers
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8172984
07/14/24 12:57 PM
07/14/24 12:57 PM
|
Joined: Aug 2011
Posts: 47,957 james bay frontierOnt.
Boco
trapper
|
trapper
Joined: Aug 2011
Posts: 47,957
james bay frontierOnt.
|
I built a skinning shed/workshop,insulated it,and put on a tin roof. I put strapping directly over the rafters and put fibreglas batt insulation between the rafters.There is an airspace about 2 inches between the tin roofing and the insulation that can vent. It gets cold here in winter and I heat it with a woodstove and havent had any problems with condensation. I did not use any vapour barrier and it hasnt been a problem. Dont know if that would work on a home sized structure.
Forget that fear of gravity-get a little savagery in your life.
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8173086
07/14/24 02:58 PM
07/14/24 02:58 PM
|
Joined: Dec 2014
Posts: 2,719 Tug Hill, NY
Squash
trapper
|
trapper
Joined: Dec 2014
Posts: 2,719
Tug Hill, NY
|
Doesn’t mater what you use plywood, perllins , OSB, etc. . But put some sort of vapor barrier on top of it and then metal roofing. Otherwise you will have condensation dripping.
Last edited by Squash; 07/14/24 02:59 PM.
|
|
|
Re: Metal roof question
[Re: Squash]
#8173092
07/14/24 03:08 PM
07/14/24 03:08 PM
|
Joined: Dec 2006
Posts: 22,132 SEPA
Lugnut
trapper
|
trapper
Joined: Dec 2006
Posts: 22,132
SEPA
|
Doesn’t mater what you use plywood, perllins , OSB, etc. . But put some sort of vapor barrier on top of it and then metal roofing. Otherwise you will have condensation dripping. Yes, you will. It must not be a thing in less humid climates like the northwestern US. But here on the east coast condensation inside unheated buildings with exposed steel roofs is common. Anybody that says it ain't hasn't been paying attention.
Eh...wot?
|
|
|
Re: Metal roof question
[Re: patrapper1989]
#8173104
07/14/24 03:28 PM
07/14/24 03:28 PM
|
Joined: Dec 2009
Posts: 22,565 The Hill Country of Texas
Leftlane
"HOSS"
|
"HOSS"
Joined: Dec 2009
Posts: 22,565
The Hill Country of Texas
|
I didn't ask any of the people who's metal roofing failed after just 15 years what they thought of it after just 2 or 3 years but I am sure they would have said it seemed fine. Time will tell.
�What�s good for me may not be good for the weak minded.� Captain Gus McCrae- Texas Rangers
|
|
|
|
|